    Re: Low discharge issue

    Where abouts along the discharge pipe is the temperature being measured? and is that with your meter or the units sensor?

    Are the water and brine circuits just one heat exchanger piped to another with only a pump and connecting pipes? or is there any additional exchangers or valves that might by-pass flow or introduce or remove heat?

    Is the brine flow also at the 1.85m3/hr? and is that only at a 2K diff?

    With steady running of the unit, is the EEV running at a steady position or varying?