    Re: saving removing the an economizer

    Renata,
    You would not waste money on it unless you really need the extra capacity.
    -6sst
    25sct
    without 2020kw absorbed power 323kw
    with 2076kw " " 319kw

    you get extra 56kw of refrigeration & draws less absorbed power.

    Set compressor to "L" port for most efficient compression ratio if not already.

    As far as what consultant say's, still don't understand what they are referring to.

    If you keep condensing pressure down as low as practical, you also get more capacity out of compressor with lower power input as well.
    Last edited by RANGER1; 27-07-2017 at 10:00 PM.

  2. #2
    Join Date
    Sep 2016
    Location
    Brazil
    Posts
    27
    Rep Power
    0

    Re: saving removing the an economizer

    Quote Originally Posted by RANGER1 View Post
    Renata,
    You would not waste money on it unless you really need the extra capacity.
    -6sst
    25sct
    without 2020kw absorbed power 323kw
    with 2076kw " " 319kw

    you get extra 56kw of refrigeration & draws less absorbed power.

    Set compressor to "L" port for most efficient compression ratio if not already.

    As far as what consultant say's, still don't understand what they are referring to.

    If you keep condensing pressure down as low as practical, you also get more capacity out of compressor with lower power input as well.
    I agree, I am trying to have some answer from the consultant, if I have any I let you know.