20-08-2009, 12:26 AM #1
-
20-08-2009, 12:42 AM #2
Re: Refrigeration 101
No, it would not be incorrect, but it may not tell you what you need to know.
The ideal is to have solid liquid at the TXV inlet, but to not back liquid up into the condenser.
Since there is solid liquid at 10-15F/5.5-8.5K SC, we can tell where along the liquid line there is solid liquid and where there is excess SC.
Excess SC is fine at the TXV inlet, but if there is excess SC at the receiver outlet, then we start backing liquid up into the condenser, which drives up the high side pressure.
Measuring SC at the TXV inlet can tell you if there is sufficient refrigerant to feed the coil, but it doesn't tell you if the system is overcharged. That's why I want to check it closer to the receiver.Last edited by Gary; 20-08-2009 at 12:51 AM.
-
20-08-2009, 10:43 AM #3
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Refrigeration 101
Some terminology clarification:
http://sporlan.jandrewschoen.com/Col...erminology.pdf
http://sporlan.jandrewschoen.com/Col...00%20Terms.pdfLast edited by nike123; 20-08-2009 at 11:18 AM.