Results 1 to 24 of 24
Thread: Howden wrv163 lube oil pressure
08-11-2017, 08:20 PM #1
Re: Howden wrv163 lube oil pressure
Any chance of a few pictures of compressor nameplate, oil going into compressor & oil pump?
LOPD is it just an alarm? or do you mean compressor stops on this.
Has oil temperature always been 130F?
Is oil cooler water cooled, has it been serviced, cleaned etc.
Is there any other relief valves in oil system after pump?
Has anything else changed over the last year, like problem started after a service like oil change or production change?
As Tycho instructs, says close oil injection a bit & problem will be probably solved.
See what it's set at first, then make adjustment.
I don't think it even needs it, not sure on 163, but all other WRV is injected under shaft seal area.
8-11 ppm iron is nothing as long as it stays at similar reading over time.
Ok something has changed but LOPD to high weather it's alarm or trip, can you adjust it down
it's still very safe.Last edited by RANGER1; 08-11-2017 at 10:18 PM.
PLEH2EREH: Since you said the oil dP has gradually decreased over time, it suggest that there might be underlying reasons other than the oil injection being full open.
if someone had opened them one day, you would have noticed an immediate and sudden drop.
I'd also like to have answered the questions Ranger asked, because I have had similar issues and have had great help from Ranger.
http://www.refrigeration-engineer.co...ain&highlight=
http://www.refrigeration-engineer.co...oes&highlight=-Cheers-
Tycho