    Re: Operating Evaporative-Condensers in Extreme Winter Conditions.

    Quote Originally Posted by chilldis
    ... when the air temperature falls below 25 f the water pumps lock out until the air temp rises above 28 f so far I have not had any ice related issues.
    I believe it is better to have the pumps ON and the fans OFF in the temperatures described above. These are not extreme temperatures by any means.

    I would not cycle the pumps for head pressure control especially in these moderate or warmer temperatures as you risk increased scale formation on the condenser coil.
    If all else fails, ask for help.


  2. #2
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Operating Evaporative-Condensers in Extreme Winter Conditions.

    Quote Originally Posted by US Iceman View Post
    I believe it is better to have the pumps ON and the fans OFF in the temperatures described above. These are not extreme temperatures by any means.

    I would not cycle the pumps for head pressure control especially in these moderate or warmer temperatures as you risk increased scale formation on the condenser coil.
    Sometimes, axial fan blades can be frozen at sub zero temperatures.

Similar Threads

  1. water? Evaporative Condensers
    By samiam in forum System Optimization
    Replies: 4
    Last Post: 26-10-2007, 06:07 PM
  2. Evaporative condensers
    By US Iceman in forum NH3
    Replies: 2
    Last Post: 05-10-2005, 01:27 AM
  3. Evaporative Condensers info
    By Tomás in forum Technical Discussions
    Replies: 4
    Last Post: 31-05-2004, 08:28 AM
  4. Evaporative Condensers info
    By Tomás in forum New Technologies
    Replies: 1
    Last Post: 09-05-2004, 07:26 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •