10-01-2007, 12:26 AM #1
Re: Minimum discharge pressure for ammonia systems
Originally Posted by Sergei
The gas flowing out of the defrost regulator adds to the compressor load (booster if the hot gas returns to the booster suction, or to the high stage if the condensate line is piped back to the intercooler).
Since the defrost pressure is around 75 to 90 psig ( 5.2 to 6.2 bar g), it would make sense to have the condensate piped back to either, a separate vessel with a separate recip. compressor, or a controlled pressure receiver. Whatever is close enough to work.
Pumping out ammonia evaporators is a pain for the reason stated. It's the same problem with trying to get a flooded out screw started. A little bit of ammonia takes a lot of heat.
-
10-01-2007, 12:47 AM #2
Re: Minimum discharge pressure for ammonia systems
US Iceman;
I had never thought about the concept of using a separate Compressor. Has this been done before, could you elaborate?
On the subject of Flooded Screws, one of our Customers managed to fill up a Screw Booster with NH3 the other day. It took 3 days to get it going again. They now believe in the safety Shutdown on the LPR we wanted to install.
-
10-01-2007, 02:12 AM #3
Re: Minimum discharge pressure for ammonia systems
HI NH3LVR,
What I'm thinking about is to use a separate vessel (accumulator if you will) to collect the gas and liquid from the defrost regulators. If the suction pressure on the compressor attached to this vessel is running higher than any other house suction pressure, it just means the penalties for hot gas defrost would be much less.
In other words, we are taking the condensate up to as high as pressure as we possibily can. From that point, a separate compressor could run the suction pressure with no problem (especially a recip).
I've seen controlled pressure receivers run this way, so it should not be any big jump in logic to say try this for defrost.
The trick would be to size the compressor to handle the defrost loads accurately. This is just me thinking out loud. I have not done this for defrost, but I can't see why it wouldn't work.
Originally Posted by NH3LVRLast edited by US Iceman; 10-01-2007 at 02:14 AM. Reason: editing
-
11-01-2007, 01:50 AM #4
Re: Minimum discharge pressure for ammonia systems
Frequency of defrosting is another important factor of refrigeration plant optimization. Right now, here in Ontario, one cold storage has defrosting once per week, but another one has defrosting twice per day. I found that overdefrosting is common problem for many refrigeration plants. It is difficult to justify additional compressor installation, if you have defrosting once per week.
Sergei
-
11-01-2007, 03:14 PM #5
Re: Minimum discharge pressure for ammonia systems
Originally Posted by Sergei
The concept I posted earlier is just one way of dealing with an issue. Just like in troubleshooting, there is always a cause and effect we need to account for in any instance.
-
11-01-2007, 04:42 PM #6
Re: Minimum discharge pressure for ammonia systems
Frequency of defrosting is another important factor of refrigeration plant optimization. Right now, here in Ontario, one cold storage has defrosting once per week, but another one has defrosting twice per day. I found that overdefrosting is common problem for many refrigeration plants. It is difficult to justify additional compressor installation, if you have defrosting once per week.
What Sergei mentions about defrosts going from twice per day to once per week has become quite typical in plants that incorporate smarter controls and/or keener operators. Evaporators that require 2 defrosts per day during that one hot week in august can often get away with one or two defrosts during the winter months. This gets back to the problem of fixed setpoints often being the “worst case” setpoint. If two or three defrosts are needed in the summer, that’s where the pins are left in the time clock. If -25 suction kept the rooms cold in August, that’s where the suction is left all year. If one evaporator requires 145# for defrost, that’s where the pressure switches are set. It’s obvious that a lot of systems have a lot of room for energy usage improvements
Another great up-side to long durations between defrosts is you can float the head pressure lower for a longer period of time thus enhancing energy savings.
Brad
-
11-01-2007, 04:57 PM #7
Re: Minimum discharge pressure for ammonia systems
Originally Posted by Bradford
Similar Threads
-
Liquid Overfeed Systems
By US Iceman in forum NH3Replies: 151Last Post: 08-03-2007, 05:34 AM -
TEV range & minimum pressure diff issue
By Lc_shi in forum FundamentalsReplies: 2Last Post: 24-04-2006, 04:32 PM -
Energy Savings
By arkay in forum IndustrialReplies: 6Last Post: 17-03-2006, 12:36 PM -
Building a wine cabinet
By Rory in forum Technical DiscussionsReplies: 38Last Post: 13-07-2004, 08:28 PM