    Re: Fujitsu-General Fault

    Ok been back. I got mucho info.

    Serial Signal Test (First diagram posted by Nike)
    Between terminal 1-3 170-200V. I think this is too high as the diagram says 70-130V.

    AFM Test: (As the second diagram posted by Nike)
    + - 360KΩ (correct)
    - N1 0.3Ω
    P + 330KΩ
    L1 L2 361KΩ
    P N1 0.3Ω
    L1L2 Control ∞
    L2 N2 ??? (I could not find the N2 terminal)
    L2 P 0.3Ω
    p L2 0.3Ω

    All these bar the first and test to the control box are nowhere near what they should be
    As a side note, I tested the leads on the multi-meter and they read 0.3Ω.

    Finally the fan motor. The motor is not the same as the one posted by Nike. I posted the winding readings earlier in this thread.
    This is what I have.


    So after all this I think the AFM is screewed. Do we all agree?

  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Fujitsu-General Fault

    Quote Originally Posted by airefresco View Post
    So after all this I think the AFM is screewed. Do we all agree?
    Agree! ....

Similar Threads

  1. fujitsu vrf fault
    By leegally1983 in forum Trouble Shooting
    Replies: 8
    Last Post: 05-09-2008, 03:13 PM
  2. Fujitsu AUY25 Fault
    By Radlam in forum Air Conditioning
    Replies: 9
    Last Post: 12-05-2008, 01:52 AM
  3. 01 fault on fujitsu
    By pacman in forum Trouble Shooting
    Replies: 7
    Last Post: 04-11-2007, 07:25 AM
  4. Fujitsu AOT24PMAL Fault Codes
    By johnmart in forum Trouble Shooting
    Replies: 5
    Last Post: 19-04-2004, 06:39 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •