    sanyo vrf



    hi
    have a vrf system that has a caution sign displaying on all controllers connected, is therea way of finding out whats wrong? suspect it might be short

    any ides philip



  2. #2
    Join Date
    Dec 2005
    Location
    Manchester England
    Posts
    19
    Rep Power
    0

    Re: sanyo vrf

    Unit has gone into auto backup mode. Inverter compressor has been disabled. Try resetting by isolating outdoor power. If problem persist, check inverter compressor and inverter.

  3. #3
    Join Date
    Mar 2008
    Location
    USA
    Age
    52
    Posts
    98
    Rep Power
    17

    Re: sanyo vrf

    Quote Originally Posted by philjd26 View Post
    hi
    have a vrf system that has a caution sign displaying on all controllers connected, is therea way of finding out whats wrong? suspect it might be short

    any ides philip
    In some situations, auto address may have not been completed. A caution icon will display on all controllers in this circumstance.

    Has this system ran in the past, or is a new start-up? You may want to dis-connect power both Indoor and Outdoor and re set the entire system. Once power has been applied ...try auto address again....allow LED 1 and 2 to go completely out. If they are both out and not flashing together....try running the system.

    Hope this helps,
    Husky

  4. #4
    Join Date
    Feb 2007
    Location
    SIDE OF THE ROAD
    Posts
    263
    Rep Power
    18

    Re: sanyo vrf

    hi still having no joy with this problem...i have 3x vrf connected in common, i check alarm outdoor leds,all leds off....

    i checked all inverters diodes, transistors and windings for balance... all seem good,

    any ideas ?/
    Last edited by philjd26; 04-12-2008 at 10:24 AM.

  5. #5
    Join Date
    Apr 2006
    Location
    stafford
    Age
    42
    Posts
    985
    Rep Power
    19

    Re: sanyo vrf

    Quote Originally Posted by sigorst View Post
    Unit has gone into auto backup mode. Inverter compressor has been disabled. Try resetting by isolating outdoor power. If problem persist, check inverter compressor and inverter.

    read your PM's !!!!!
    Paul


    "KEEP IT COOL"

  6. #6
    Join Date
    Jul 2005
    Location
    Ireland
    Age
    56
    Posts
    164
    Rep Power
    19

    Re: sanyo vrf

    HI Philjd,

    Swill is correct Inverter compressor has shut down for some reason

    Could be any of the following

    Faulty HIC PCB
    Loose conection on PCB or Compressor
    (we'll assume you have checked all the basics)
    Low on gas on full load compressor may overheat Discharge temp above 108-111 degrees C.
    Pumpdown due to an SVK connected to an indoor not opening.

    High pressure for same reason in heating

    possible faulty compressor.

    Many more reasons.

    It's easy enough to check all of the above by connecting a standard sanyo remote control to the outdoor unit on terminals 3and4 then entering the sensor check mode.

    It's possible to check all system temperatures, pressures
    and current sensors by doing this in real time.



    If you want a service manual drop me a PVT message with your email and I'll send one on to you.

    Apologies for the late reply been real busy here

    T

Similar Threads

  1. Sanyo fault codes
    By Slim R410a in forum Air Conditioning
    Replies: 3
    Last Post: 03-11-2008, 09:02 PM
  2. Sanyo system needs supplemental heat
    By mchild in forum Air Conditioning
    Replies: 2
    Last Post: 29-11-2007, 03:50 PM
  3. fault on a sanyo unit
    By marc5180 in forum Air Conditioning
    Replies: 7
    Last Post: 18-08-2007, 11:04 PM
  4. Sanyo inverter split unit
    By cikku in forum Domestic
    Replies: 3
    Last Post: 22-05-2006, 06:07 PM
  5. Sanyo equipment
    By Karl Hofmann in forum Air Conditioning
    Replies: 6
    Last Post: 17-09-2004, 08:39 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •