Re: R404a water cooled condensing unit with 8oC cooling water
Don't understand why you subtract twice 10K and uses twice evaporation. When refrigerant is leaving your evaporator, it's all evaporated as a superheated gas.
You evaporate at -30°C, 10 K superheat is too much, 7K, so -23°C leaving evaporator and +/- 10K along suction line = -13°C inlet compressor
Select compressor for -30°C and 20K total SH and your evaporator at -30°C and 7K SH.
1. You don't need a receiver but charge is then somehow critical. You can install one but it isn't necessary.
And you will not see low condensing pressures, the WVFX will maintain a stable HP.
I feel you still doesn't get the whole picture.
Perhaps this will help http://www.danfoss.com/NR/rdonlyres/.../PFD00A102.pdf
2. If you have pump down, no CCH needed. As you said, it's hot enough in your country to omit a CCH. The temperature of the returning gas has nothing to do with the need for a CCH.Last edited by Peter_1; 12-01-2014 at 03:31 PM.
It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
12-01-2014, 05:47 PM #2
Re: R404a water cooled condensing unit with 8oC cooling water
Sorry for my unclear statement. It's water cooled condensing unit for cold and chiller room.
First is for meat and sea food so they have -30 oC evaporation and -23 oC cold room temperature with suction gas temp -20oC for 10oK super heat
Second is a for higher condition (vegetable, beverage,....) so they have -10 oC evaporation and 0oC suction gas temp. (10o SH also) like compressor selection data This for worst case Maybe it's T evaporation will be raised up if have other requirement.
For SH calulation : for +10 oK along suction line as you said, could i avoid it because if suction line exposed to air room, we will have frost. i want to insulated it.
I have no experience with refrigerant line cause nearly all of my work before come with HVAC system so most of refrigeration work come from chiller's manufacture guys. and it's completely different condition with HVAC chiller. May be it's not all but i'm very appreciated your supports.
Thank alot