    Call out to Toshiba wall unit RAV-SM562KRT-E not heating.
    While cycling through the controller the heat symbol is missing and went into the system configuration menu, 0F-heat mode to select available but after saving this setting and going into the config. the controller shows 0001 unavailable
    The controller is RBC-AM31e
    I'm Stuck.. any advice


    FIXIT............first time every time

  2. #2
    Join Date
    Feb 2017
    Location
    UK
    Posts
    117
    Rep Power
    9

    Re: Toshiba wall unit lost ability to heat

    I dont know much about Toshiba units, but i do have a service manual for the above unit which i can send over to you in pdf if that would be any help?

  3. #3
    Join Date
    May 2006
    Location
    Hayling Island, UK
    Age
    60
    Posts
    143
    Rep Power
    21

    Re: Toshiba wall unit lost ability to heat

    Hi FIXIT,

    In my opinion there are three menus you need to check \ set up for all modes to be available.

    0d = 0000 (auto mode available)
    0F = 0000 (heat mode available)
    2d = 0015 (all modes available)

    GT Phelans in Bray should be able to help you - they're the Toshiba distributor for Eire

    Regards
    Loops

  4. #4
    Join Date
    Sep 2005
    Location
    Granard, Ireland
    Age
    55
    Posts
    43
    Rep Power
    0

    Re: Toshiba wall unit lost ability to heat

    Quote Originally Posted by Loops View Post
    Hi FIXIT,

    In my opinion there are three menus you need to check \ set up for all modes to be available.

    0d = 0000 (auto mode available)
    0F = 0000 (heat mode available)
    2d = 0015 (all modes available)

    GT Phelans in Bray should be able to help you - they're the Toshiba distributor for Eire

    Regards
    Loops
    Thanks folks
    It is a single system
    changed 0F to 0000 but it will not save that change.
    i will put it down to faulty indoor board.
    thanks.