30-04-2010, 09:29 AM #1
I have failure message on a trane SMM Module.
Can anyone help me with this, It is probably a communication problem. I don't have the user manual.
The fault message that is flashing in the display is: A Com I/04.
Please help.
30-04-2010, 11:48 AM #2
Re: I have failure message on a trane SMM Module.
How many SMM modules does your chiller have?
If it's 3 or less, ignore the message.
It's generated because the main card is trying to communicate with card 4 and not getting a reply.
A standard scroll chiller with 2 circuits will have a main card - the one with the display - and 2 smaller cards with a similar but square black cover & no displays. the second is circuit 2 control, and the third is the condenser fan control.
the fourth card is just an options card, which as far as I know almost no-one in the U.K. ever specified.
It is possible to stop the message by altering the machine configuration setting, but I'm afraid that's in the area of software only accessible to a Trane technician (or ex Trane tech. of course).
If you don't have the 4th card, the alarm will not affect the running of the chiller & as I said earlier, can safely be ignored.
Otherwise you'll need someone like me or a Trane technician to sort it. Ditto if you do have a fourth card.
30-04-2010, 11:22 PM #3
hi janbanan ive emailed you smm user instructions
02-05-2010, 05:24 AM #4
Carrier Transicold Container Problem
By Shamel in forum TransportReplies: 39Last Post: 24-01-2012, 12:23 AM -
Trane CXAH/CGAH-240 problem
By MortenOlsen in forum Trouble ShootingReplies: 7Last Post: 12-05-2010, 08:49 PM -
AEC Pinical chiller with trane comp
By cptrdbrd in forum CommercialReplies: 1Last Post: 28-10-2009, 10:47 PM -
Problem with Trane RTAD100 chiller.
By on4hf in forum Trouble ShootingReplies: 8Last Post: 14-10-2009, 09:01 PM -
SR2 50 models electric SBY diagonostics made simple
By absolute-zero in forum TransportReplies: 5Last Post: 04-01-2008, 06:11 PM