    Re: r410a Scroll Chiller Cooling Performance Problem-Expert advise please

    Quote Originally Posted by AliCanGonc View Post
    Dear Ranger,

    Yes i have a sight glass on the liquid line, i see small bubbles but %90 liquid feeded to EXV
    Liquid receiver?

    The only things I can think of with your symptoms are,

    - System 2 short of refrigerant.
    - no liquid receiver or low level in it. Has to have one in my opinion.
    - change filter drier to eliminate pressure drop & possible flash gas after it due to little sub cooling.
    - Expansion valve open more as starving for refrigerant.
    - superheat 7 degC possibly fooling us due to it only being able to get a maximum of that, unless ambient can increase it through heat gain which does not apply in your situation on test rig.
    - If system short of refrigerant condenser may behave differently & condense at a higher pressure.

    Does not explain higher suction pressure but running out of ideas.