    Fitting drier to receiver



    Dear Friends

    Can anyone give me a good reason why a filter drier cannot be fitted directly to the receiver liquid discharge or very close to it at low level.


    Thanks



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Fitting drier to receiver

    The filter\drier should be on the liquid line before the sight glass and SV.
    It should be connected so it will be comfortable to replace it when necessary.
    If you want to fit it directly on the receiver, I don't see any reason why not.

  3. #3
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: Fitting drier to receiver

    Hi Contactor
    As close as possible with isolation valves either side yes!
    Otherwise you have a receiver full of liquid to deal with?
    So as long as you have an isolation valve before the filter, "Why Not!"
    In some instances and dependant upon the system design a bypass pipe or second filter is useful to allow
    Filter changes without plant shutdown?
    Grizzly

  4. #4
    Join Date
    May 2007
    Location
    Scotland
    Posts
    327
    Rep Power
    17

    Re: Fitting drier to receiver

    Thank you some good points there. I wondered about the accumulation of excess oil has anyone come across that as a problem before? I don't remember seeing a drier in that location before.

  5. #5
    Join Date
    Jun 2010
    Location
    Yorkshire
    Age
    58
    Posts
    522
    Rep Power
    19

    Re: Fitting drier to receiver

    I was once told never to fit them in an upward orientation (flow arrow up), but only in the downward orientation from the reciever (flow arrow down). When fitted in an upward orientation the liquid can expand and cause unwanted bubbles, especially if its an oversized dryer.
    Training may be finished but experience is never complete.

  6. #6
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Fitting drier to receiver

    Quote Originally Posted by chilliwilly View Post
    the liquid can expand .
    Nope, liquid can not expand, only gas.

  7. #7
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,762
    Rep Power
    32

    Cool Re: Fitting drier to receiver

    Fitting the drier in a down flow direction ensures an even distribution of liquid, and full use of your drier. Driers fitted horizontally in say a suspected contaminated system... might have the lower half of your drier doing all the work and causing a pressure drop.

    Some of the OZ imported kits have the drier fitted horizontally after the Receiver.
    Either way, on a new Cold-room or a Freezer room install, i fit a Suction line drier.

    BTW, my comment has bugger all to do with Liquid line Drier location.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  8. #8
    Join Date
    Jun 2010
    Location
    Yorkshire
    Age
    58
    Posts
    522
    Rep Power
    19

    Re: Fitting drier to receiver

    Yet the reciever contains liquid and gas?
    Training may be finished but experience is never complete.

  9. #9
    Join Date
    Jun 2010
    Location
    Yorkshire
    Age
    58
    Posts
    522
    Rep Power
    19

    Re: Fitting drier to receiver

    Quote Originally Posted by chemi-cool View Post
    Nope, liquid can not expand, only gas.
    Yet the reciever contains liquid and gas?
    Training may be finished but experience is never complete.