    Re: Evaporating / condensing temperatures

    The values you reference for 1%, 3% & 5% were revised sometime ago by ASHRAE. The new occurence values are 0.4%, 1%, & 2% and account for the percentage of annual hours where that value is exceeded.

    So, this equates to:

    0.4% X 8760 hours = 35.4 hours
    1.0% X 8760 hours = 87.6 hours
    2.0% X 8760 hours = 175.2 hours

    In some locations the dry bulb temperature may not vary much, in other locations it will.

    I'm late to this discussion, but I'm sure it has been lively with lana participating.
    If all else fails, ask for help.


  2. #2
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Evaporating / condensing temperatures

    Thank you US Iceman for clarifying the percentages.

    Cheers
    Even Einstein Asked Questions

  3. #3
    Join Date
    Mar 2006
    Location
    Malaysia
    Age
    48
    Posts
    233
    Rep Power
    19

    Re: Evaporating / condensing temperatures

    Quote Originally Posted by US Iceman View Post
    The values you reference for 1%, 3% & 5% were revised sometime ago by ASHRAE. The new occurence values are 0.4%, 1%, & 2% and account for the percentage of annual hours where that value is exceeded.

    So, this equates to:

    0.4% X 8760 hours = 35.4 hours
    1.0% X 8760 hours = 87.6 hours
    2.0% X 8760 hours = 175.2 hours

    In some locations the dry bulb temperature may not vary much, in other locations it will.

    I'm late to this discussion, but I'm sure it has been lively with lana participating.
    Ok thank you for this data, i have seen it on http://www.microcool.com/cooling/bro...PreCooling.pdf.
    However, i am so happy that i was a reason of correcting the common perception of the fellows for using maximum ambient temperature occurred in the year as the design temperature for the condenser without looking to something named the frequency occurrence. Regardless of these new values i do believe as u mentioned each location has its specifications.

    Cheers

  4. #4
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Evaporating / condensing temperatures

    Hi there,

    In Persian Gulf area we have minimum of three months extreme temperatures between 45 to 55°C.

    3 months x 30 days x 24 hrs = 2160 hrs

    This is way more than 1% occurrence.

    Cheers
    Even Einstein Asked Questions

Similar Threads

  1. CARE refigerants by BOC
    By dogma in forum Refrigerants
    Replies: 8
    Last Post: 23-03-2010, 12:39 PM
  2. This a long one - AKV
    By Peter_1 in forum Industrial
    Replies: 6
    Last Post: 26-12-2008, 11:47 AM
  3. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  4. evaporating temperatures
    By MrsFreeze in forum Fundamentals
    Replies: 11
    Last Post: 31-05-2007, 02:15 AM
  5. Condensing temperatures with ammonia
    By Friobernal in forum Technical Discussions
    Replies: 2
    Last Post: 12-07-2002, 02:50 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •