    Re: Replacement fo CO2 Bulk Tank refrigeration unit

    Hi, NH3LVR

    Quote Originally Posted by NH3LVR View Post
    If I understand you are thinking of running relief valves back to another part of the system.
    This used to be common. I inventoried relief valves in a plant a couple of weeks ago and found some that way.
    Vilter piston machines do this internally.
    The problem you face is that the relief valve opening pressure becomes the difference between the pressure you are trying to relieve and where you are relieving to. In other words, if you have a relief valve set at 250lbs (17.2 BAR) discharging into a low pressure vessel with a 150lbs (10.3 BAR)relief the worst case conditions would mean a valve opening At 400lbs (27.6BAR).
    These would be extreme conditions, such as a fire, but this might be when you need them most.
    I also believe this might make the other reliefs undersize in the plant.
    About Vilter I do not know, seems good construction but I know some other piston compressors having similar system like protection against liquid stroke.

    I was thinking to relief high (condensing) pressure to low pressure vessel working at -20C/-30C/-45C even -10C and then maybe from that vessel relief valve to atmosphere.

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  2. #2
    Join Date
    Jul 2006
    Location
    USA
    Age
    74
    Posts
    865
    Rep Power
    26

    Re: Replacement fo CO2 Bulk Tank refrigeration unit

    Quote Originally Posted by Josip View Post
    About Vilter I do not know, seems good construction but I know some other piston compressors having similar system like protection against liquid stroke.

    I was thinking to relief high (condensing) pressure to low pressure vessel working at -20C/-30C/-45C even -10C and then maybe from that vessel relief valve to atmosphere.
    Josip:
    I apologize as I believe I was unclear.
    I only mentioned Vilter as they are a example of internally relieving pressure that is considered acceptable. The function in the Vilter is too prevent high pressure in case the machine is started with the discharge valve closed. It doubt it would be of much use in a liquid slugging situation.
    My comments were directed to your post as I understand it.
    Again my apologies for being unclear.

  3. #3
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Replacement fo CO2 Bulk Tank refrigeration unit

    Hi
    both Sabroe and Grasso recips have this relief fitted

    If you are fitting PRV's to vent back to suction they have to be outlet independant, uneffected by the pressure at the outlet side, most common PRV's are not

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  4. #4
    Join Date
    Jul 2006
    Location
    USA
    Age
    74
    Posts
    865
    Rep Power
    26

    Re: Replacement fo CO2 Bulk Tank refrigeration unit

    Quote Originally Posted by Andy View Post
    If you are fitting PRV's to vent back to suction they have to be outlet independent, unaffected by the pressure at the outlet side, most common PRV's are not
    Andy;
    Do you have a example of a PRV that is not not outlet dependant? I have never seen one for refrigeration use. We have a job coming up soon (NH3) on which we could save a great amount of time and trouble if we could use them in a couple of places. I assume the other valves would have to be increased in size to accommodate them?

  5. #5
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Replacement fo CO2 Bulk Tank refrigeration unit

    Hi NH3LVR

    Herl make some (now owned by Parker) Danfoss has a range, using a pilot and main valve assembly.
    I will take a look at the Danfoss site and see if I can get a link.

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  6. #6
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Replacement fo CO2 Bulk Tank refrigeration unit

    Hi NH3LVR

    Please use the following linkhttp://www.danfoss.com/Products/Cate...972d837cf1a%7d

    Some link

    POV valve is the one

    Kind Regards Andy