Re: 9 superheat & subcooling scenarios
The thing to mention in the Original Posts list of scenarios,
If your system is capillary or fixed orifice, superheat is the measurement you need to get right,
For t/x valves you need to get your subcool right.
-
17-10-2010, 04:51 PM #2
Re: 9 superheat & subcooling scenarios
-
17-10-2010, 09:18 PM #3
Re: 9 superheat & subcooling scenarios
Cheers Gary.
It makes a bit of sense now.
The chiller had a large approach temp of 9-10°C, but it also had a low superheat of 2°C.
This meant the shell+ tube evap was not producing anough heat transfer which concluded was due to the concentration of glycol which the customer could not tell us and i didnt have the correct tool.
What i dont understand is - if you have low subcool it means the liquid is not staying in the condenser long enough to cool, would this also mean you have a low head pressure? But if you have inverter fans controlling head pressure then this should be o.k. resulting in normal subcool?
I think i,m starting to confuse myself again.
I totally understand. Suction superheat and discharge superheat but somehow cannot get to grips with subcool 100%.
Anyone shed some light?
Similar Threads
-
Superheat and Subcooling
By Chunk in forum FundamentalsReplies: 42Last Post: 15-01-2011, 01:24 AM -
subcooling and superheat are standard measurement or not?
By karl2009 in forum Technical DiscussionsReplies: 3Last Post: 10-01-2009, 11:39 PM -
Help on superheat and subcooling
By hvac student in forum Trouble ShootingReplies: 8Last Post: 08-08-2008, 02:25 PM -
Subcooling at TEV vs Superheat at Compressor relation in Steady State
By GXMPLX in forum FundamentalsReplies: 12Last Post: 14-07-2008, 03:00 PM -
Superheat and subcooling
By marc5180 in forum TrainingReplies: 27Last Post: 08-10-2007, 09:21 PM