    Re: Refrigeration 101

    Quote Originally Posted by chillyblue View Post
    How high is high, 8, 10 ,20, 30, 50???????????
    and if it is high what indication can you get from the evap that it is performing correctly,
    Your indication comes from the condenser. Given a normal load, and assuming good condenser airflow, the SCT should be 20-35F/11-19K above the ambient (condenser air in) temperature (20-35F/11-19K cond TD), depending upon the relative coil sizing. If the heat load being rejected by the condenser is normal, then the heat load being absorbed by the evaporator must also be normal.