Re: Daikin VRV 3 pipe changing mode
Multi,
It sounds like you’ve had one of those days
At least you didn’t need to dig your way through the snow to get up the street on the way home
U4 errors can be real pain on older installs, especially when it’s an intermittent fault.
You will probably be aware of the most common reasons for a U4;
- Mains power off at indoor/bs/outdoor
- Loose live or neutral connection
- Mains power has been switched off/on but system fails when reinitializing (turn power off/on again and hold down reset button for 10sec)
- Bad connection on F1F2 comms lines
- Mice or rats chewing into comms cables!
- If it’s an R22 KJ outdoor unit the small green interface pcb that f1f2 cable connects to has been known to cause probs (not applicabe for 407c).
- Faulty indoor/bs/outdoor main PCB (never had this with intermittent U4 error tho)
- K series units can be very slow to recognize a U4 error
- U4 errors will auto reset when comms are reestablished
Last edited by VRVIII; 21-12-2009 at 09:25 PM.
Similar Threads
-
MICROPROCESSOR DIAGNOSTICS/Differnces beteween TK/CTC
By REEFER-TEK in forum TransportReplies: 12Last Post: 27-03-2011, 04:12 AM -
Daikin r407c 2 pipe vrv ja fault code any offers?
By Contactor in forum Air ConditioningReplies: 11Last Post: 28-07-2009, 01:26 AM -
Measurement of pipe lengths
By batfink in forum Technical DiscussionsReplies: 11Last Post: 23-09-2008, 09:50 PM -
Thermo King OptiSet
By REEFER-TEK in forum TransportReplies: 4Last Post: 06-12-2007, 07:23 PM -
TK basic micro-p features and functions
By REEFER-TEK in forum TransportReplies: 0Last Post: 05-12-2007, 06:25 PM