    Danfoss Solenoid Coil



    Hi
    Has anyone else had the problem of a Danfoss solenoid coil overheating and sticking to the stem?

    If so any tips on best methods to remove them?



  2. #2
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,044
    Blog Entries
    4
    Rep Power
    31

    Re: Danfoss Solenoid Coil

    I've had that problem on a few occasions, usually with very old solenoids, where water has gotten between the coil and the stem.

    I have found that the best way to remove them is to use a pipe wrench on the coil to rotate it back and forth while applying gentle pressure from below with a large flat head screwdriver.

    it might take 5-10 minutes to work it all the way to the top, but the clue is to not use too much angular force so you don't break the thin steel on the stem.


    Hope this helps
    -Cheers-

    Tycho

  3. #3
    Join Date
    Feb 2016
    Location
    UK
    Posts
    2
    Rep Power
    0

    Re: Danfoss Solenoid Coil

    Quote Originally Posted by Tycho View Post
    I've had that problem on a few occasions, usually with very old solenoids, where water has gotten between the coil and the stem.

    I have found that the best way to remove them is to use a pipe wrench on the coil to rotate it back and forth while applying gentle pressure from below with a large flat head screwdriver.

    it might take 5-10 minutes to work it all the way to the top, but the clue is to not use too much angular force so you don't break the thin steel on the stem.


    Hope this helps
    Thank you for the advice. I resorted to being very careful will a junior hacksaw cutting away at the coil until I exposed the small ridge area on the stem. I found that the plastic of the coil assembly melted into this area an thus keying itself onto the stem.

    I had to be very careful not apply too much stress onto the body as the pipework in this area is very small and behind this is a 360kg flooded system with no means of isolation!

  4. #4
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: Danfoss Solenoid Coil

    Well Done.
    Caution is always the best policy!
    And welcome to the forum.
    Grizzly
    Despite the High Cost of Living it still remains Popular!

  5. #5
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,044
    Blog Entries
    4
    Rep Power
    31

    Re: Danfoss Solenoid Coil

    Quote Originally Posted by reynard883 View Post
    Thank you for the advice. I resorted to being very careful will a junior hacksaw cutting away at the coil until I exposed the small ridge area on the stem. I found that the plastic of the coil assembly melted into this area an thus keying itself onto the stem.

    I had to be very careful not apply too much stress onto the body as the pipework in this area is very small and behind this is a 360kg flooded system with no means of isolation!
    that sounds like a lot of patient work

    Like Grizzly said "Caution is always the best policy!"

    I hope you meant the ridge at the top, and not the ridge at the bottom, had it been a Normaly open valve

    But best of all, you used your brains, identified the issue, used common sense and fixed the problem

    Welcome to RE, and I hope we'll see you again
    -Cheers-

    Tycho

  6. #6
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Danfoss Solenoid Coil

    Reynard,
    As Tycho suggested moisture can cause burn out of coil.
    Make sure "0" ring on bottom of armature tube & secure coil on properly to seal everything.
    Otherwise solenoid could be faulty for some reason not lifting plunger, so overheating.

  7. #7
    Join Date
    Aug 2001
    Location
    Leominster, MA
    Age
    71
    Posts
    45
    Rep Power
    0

    Re: Danfoss Solenoid Coil

    Quote Originally Posted by RANGER1 View Post
    Reynard,
    As Tycho suggested moisture can cause burn out of coil.
    Make sure "0" ring on bottom of armature tube & secure coil on properly to seal everything.
    Otherwise solenoid could be faulty for some reason not lifting plunger, so overheating.
    I bumped into one of these Danfoss SOV's today, covered in blue plastic. How the hell do you take the power head off? Sporlan has a small cap that pops off the top, but this one doesn't seem to have a way to release. It spins easily, only 3years old. Any insight?
    My wife says I don't listen to her....or something like that....

  8. #8
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Danfoss Solenoid Coil

    Quote Originally Posted by hvac01453 View Post
    I bumped into one of these Danfoss SOV's today, covered in blue plastic. How the hell do you take the power head off? Sporlan has a small cap that pops off the top, but this one doesn't seem to have a way to release. It spins easily, only 3years old. Any insight?
    http://products.danfoss.com/productr...lenoid-valves/

    Id like this use lever like screwdriver to lever it directly upwards.
    Has a strong clip to hold in place.

  9. #9
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Danfoss Solenoid Coil

    20160813_225024.jpg

    Hi
    Ranger

    as you know we have these type of coil
    mbc

  10. #10
    Join Date
    Aug 2014
    Location
    UK
    Age
    75
    Posts
    508
    Rep Power
    25

    Re: Danfoss Solenoid Coil

    All the previous advice on these coils is helpful , but the cause of coil failures is often due to simple errors in coil selection or fitting. Many manufacturers for logistic reasons often only stock a couple of coil voltages but with dual frequency design. They use this coil for both UK and European systems. If we look at typical UK voltage and frequency most voltages around the UK are approx 240 vo lt 50 hz. But often to reduce their coil stocks they fit a "universal one size fits all coil" ie the 230 volt dual frequency coil 50/60 hz . Often on large sites they have there own electrical sub stations where the single phase voltage I have personally measured has been as high as 256 volts 50hz.
    If the 230 volt 50/60hz coil is fitted on a system that actually has this higher voltage supplied then the coil core temperature will climb to a point where the coil encapsulation starts to create small hair line cracks which moisture can enter into the coil winding.
    As the coil energises and de- energises the coil expands and contracts and will draw moisture into itself as it breaths.
    So we as the service engineers must fit the right coil for the actual voltage / frequency of the system. Manufacturers always keep their stock inventory as small as possible to keep costs low but often this causes coil failures due to the coil being used outside its design ratings.
    The O ring seal at the bottom of the tube is the most important part as if this is not fitted or is damaged moisture can be drawn up inside the coil, the moisture during energisation will boil and melt the encapsulation and then a melted portion of the encapsulation "normally on the front side" puuks out like a small volcano. If you look up into the hole where the armature goes , you can see the exposed flux sleeves if moisture has got into the coil then often these flux sleeves go rusty. When the coil overheats due to over voltage / dual frequency coil/ fitted to very hot discharge valve,etc this often causes the coils waterproofing fluid to weep from the flux sleeve area this is often a white substance. When the plastic encapsulation melts into the armature hole , this normally occurs when the coil is off the valve while still energised.
    Always fit the correct coil for the valve type (wattage size) and the correct voltage and frequency as measured on the site
    Never just line size a solenoid valve

  11. #11
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: Danfoss Solenoid Coil

    What a brilliant reply Glenn.
    Some really useful points
    Thank you!
    May I add that the whole UK Supply network has never ben more unstable.
    With quite large variations of voltage being experienced at times.
    Which make your observations all the more relevant.
    Grizzly
    Despite the High Cost of Living it still remains Popular!

  12. #12
    Join Date
    Aug 2006
    Location
    england
    Age
    49
    Posts
    3,874
    Rep Power
    46

    Re: Danfoss Solenoid Coil

    Heres one I found blown a while back,

    https://www.youtube.com/watch?v=0zdACXNEfCg
    Mostly found in Oxfordshire, UK :)

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •