    Re: AWHP superheat & sub-cooling

    We are testing our chillers at 55C (131F) ambient and experienced compressor overload at various points.
    Our solution was a suction line heat exchanger with a txv feed the opposite direction of the suction flow. Insulate the heck of the suction line. My suction temperature 6-9C with a below normal amp draw.
    5 ton unit 1 ton TXV.

  2. #2
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: AWHP superheat & sub-cooling

    Quote Originally Posted by micknick View Post
    We are testing our chillers at 55C (131F) ambient and experienced compressor overload at various points.
    Our solution was a suction line heat exchanger with a txv feed the opposite direction of the suction flow. Insulate the heck of the suction line. My suction temperature 6-9C with a below normal amp draw.
    5 ton unit 1 ton TXV.
    I'm thinking the same effect could be had without the heat exchanger by simply injecting the output of the TXV directly into the suction line, with the bulb mounted downstream, i.e. liquid injection.

    But once again we see that its about keeping the compressor cool.
    Last edited by Gary; 27-08-2009 at 11:58 PM.

  3. #3
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: AWHP superheat & sub-cooling

    Quote Originally Posted by micknick View Post
    We are testing our chillers at 55C (131F) ambient and experienced compressor overload at various points.
    Thanks micknick, for your very useful comment. 55'C is quite some temperature - I'd imagine this is the local ambient surroundings where the compressor is operating. What were the symptoms of the compressor overload?

    Our solution was a suction line heat exchanger with a txv feed the opposite direction of the suction flow. Insulate the heck of the suction line. My suction temperature 6-9C with a below normal amp draw.
    5 ton unit 1 ton TXV.
    So, basically a suction line cooler, using 2-phase feed out of the TXV.

    How did your evaporator respond to the rise in vapour fraction?
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

Similar Threads

  1. 9 superheat & subcooling scenarios
    By nike123 in forum Fundamentals
    Replies: 39
    Last Post: 19-07-2011, 03:16 AM
  2. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  3. Replies: 5
    Last Post: 14-09-2009, 07:33 AM
  4. Low superheat and sucooling
    By jayaeros in forum Trouble Shooting
    Replies: 23
    Last Post: 05-07-2009, 06:21 AM
  5. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •