    Re: Carters Widget Revealed!

    OK, keeping it simple, if we had NO superheat at the exit of the evap, would the flash gas in the evap have any effect on the net cooling of the room. (energy only)

  2. #2
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Carters Widget Revealed!

    Quote Originally Posted by mad fridgie View Post
    OK, keeping it simple, if we had NO superheat at the exit of the evap, would the flash gas in the evap have any effect on the net cooling of the room. (energy only)
    Yes.

    Simply put, as flash gas is reduced, 'x' will reduce (ie. less vapour in incoming 2-phase fluid) - this will increase Q'evap (refrigeration effect). (A few simplifying assumptions in this, so far)
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  3. #3
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Carters Widget Revealed!

    Quote Originally Posted by desA View Post
    Yes.

    Simply put, as flash gas is reduced, 'x' will reduce (ie. less vapour in incoming 2-phase fluid) - this will increase Q'evap (refrigeration effect). (A few simplifying assumptions in this, so far)
    Are you sure?

    I will re word. Liquid is at fixed pressure and temp (saturated). It enters the expansion valve, expands (reduction in pressure) So just before it enters the evaporator we a % of vapour by mass (weight) and a % of liquid by mass.
    If there in no pressure drop in the evap and no superheat at the exit of the evap, 100% by mass is all vapour at saturation leaving the evap.
    Does the original flash gas (that entering the evap) have any benefit to the net cooling.?

    We are looking at energy only, not effect on heat transfer co-efficients

  4. #4
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Carters Widget Revealed!

    Quote Originally Posted by mad fridgie View Post
    Are you sure?

    I will re word. Liquid is at fixed pressure and temp (saturated). It enters the expansion valve, expands (reduction in pressure) So just before it enters the evaporator we a % of vapour by mass (weight) and a % of liquid by mass.
    If there in no pressure drop in the evap and no superheat at the exit of the evap, 100% by mass is all vapour at saturation leaving the evap.
    Does the original flash gas (that entering the evap) have any benefit to the net cooling.?

    We are looking at energy only, not effect on heat transfer co-efficients
    If you split the flows as follows:
    1. Vapour only (your 'flash gas') at m'fg;
    2. Liquid only at m'l...
    3. m'r = m'l + m'fg (total flow before split)

    ... then, if we know the pressure of each stream, we can locate the individual state points as follows:
    1. Vapour - assume saturated vapour - located on right of bell;
    2. Liquid - assume saturated liquid - located on left of bell.

    If the fluids are mixed, then the mixture properties are constructed based on 'x', the vapour percentage in the mixture.

    If the vapour is transported away, then only m'l goes towards the evaporator. The net refrigeration effect (assuming fully saturated liquid) is:

    Q'evap = m'l*hfg

    Where :
    Q'evap = evaporator capacity [W]
    m'l = liquid mass flowrate [kg/s]
    hfg = latent heat of vapouraziation [J/kg]

    So, the real amount of duty [W] managed by the evaporator will depend on how much liquid is actually going to it.
    Last edited by desA; 22-08-2011 at 10:23 AM.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  5. #5
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: Carters Widget Revealed!

    Quote Originally Posted by mad fridgie View Post
    OK, keeping it simple, if we had NO superheat at the exit of the evap, would the flash gas in the evap have any effect on the net cooling of the room. (energy only)
    Right time to jump in with both feet.

    The flash gas is caused where the energy contained in the liquid refrigerant entering the TEV is used to lower the temperature of itself to get to the boiling point in the evaporator.

    i.e. Te is -30*C, Tc 35*C subcooling 5K means as ref. enters the TEV at 30*C it has to drop temperature by 60K to boil. Ideally the temperature of liquid feed to the TEV would be as low as possible as this shifts the expansion line on a PE chart over to the left into the higher % region of liquid/vapor mix. If it was 100% that means the liquid at the TEV was already at -30*C. If it was you wouldn't really need a refrigerant circuit as you somehow had the means to get refrigerant at the same temperature as Te so you'd use that means instead.

    So in answer the flash gas has no net effect in cooling the room. It only cools the refrigerant to the evaporators boiling point.

    How does that sound?

    Cheers,
    Andy.