Results 1 to 16 of 16

Thread: Heat gains

Hybrid View

  1. #1
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    38

    Re: Heat gains

    Hi Mark
    Q = m [250kg ] x 4.19 x [TD ]
    Q = 250 x 4.19 x 5 / 3600 seconds
    = 5237.50 Kj / 3600 = 1.45 Kw [ Kj/s ]

    determine flow rate 0.25Kg/sec or litres /sec = 3.3 gallons per second TOO high, more like 0.02 L/sec.

    Q= 0.02 x 4.19 x 5'c td = 0.42 Kw duty

  2. #2
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Heat gains

    Quote Originally Posted by Magoo View Post
    Hi Mark
    Q = m [250kg ] x 4.19 x [TD ]
    Q = 250 x 4.19 x 5 / 3600 seconds
    = 5237.50 Kj / 3600 = 1.45 Kw [ Kj/s ]
    determine flow rate 0.25Kg/sec or litres /sec = 3.3 gallons per second TOO high, more like 0.02 L/sec.
    Q= 0.02 x 4.19 x 5'c td = 0.42 Kw duty
    Hi Magoo thanks for that.

    When I was working out the cooling load originally I didn't divide by the 3600 seconds (1 hour) as I wasn't sure wether I needed to do this or even wether I should have divided by 24hours (86,400).

    The flow rate of 0.02 and the KW seems much better now although the pulldown time has increased to 208mins.
    The difference between genius and stupidity is that genius has its limits.

    Marc

Posting Permissions