21-02-2010, 03:17 PM #1
Re: Capillary tube size, refrigerant, oil
^ That is quite a remarkable picture.
Can I ask why you are using so many capillaries, & not a TXV?Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
21-02-2010, 03:42 PM #2
Re: Capillary tube size, refrigerant, oil
Because of the :
Efficiency
Cost
Efficiency Again - No Valve can match the cappilary in efficiency.
Rapid balance of the system
No malfunctions , No orifice
Well many more ...
And because I have tried the TXV's without having the same results.
But results for each one of us different ... So for me the capillary is the one.
-
21-02-2010, 04:52 PM #3
Re: Capillary tube size, refrigerant, oil
Very interesting.
I'm finding the capillary to be very challenging. For small power systems, it's difficult to get a TXV anyway - they are also expensive. It is going to be worth the time & effort to get to understand these fascinating parts of our toolbox.
How do you see the cap tube working for a heat-pump, with the large spread in Tc,sat from cold to hot condition?Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
21-02-2010, 05:52 PM #4
Re: Capillary tube size, refrigerant, oil
I have never tried to work capilary on a heat pump.
However my opinion is the target with the Cap is to make the LOW PRESSURE decreases as possible even in 40C work conditions. As mentioned before the Tcsaturation and/or superheats, subcooling and all the book of thermodynamics can be manipulated else way. As mentioned in previous posts for R22 and R404A this can be done with Presure switches to control the fan. Also the use of more capilaries instead of one, the quantity of refrigerant, a receiver , fan rpm, fan pitch, Diam of fan, condensing unit and many more...
What I am thinking now is that the Cap on a heat pump might and should work different since the system advantages from the HOT PLATE - not the cold.
So the more HP in the Hot plate (that in standard systems is the cold plate) the more of the benefit...
So we are talking for a smaller condenser and bigger in length capillary... Then wll need some more fluid in it, but will change the thermodynamics once more...
So you need a small receiver in order to store the excess of the refrigerant fluid.. Receiver can be a small filter of let say 60gram as the excess of refrigerant should only be a +25gr ~ 50gr.
I refer ,as have in mind an older htread of yours, to the system have in your lab and the rest of the members gave a fantastic analysis and manipulation of DANFOSS programs...
The noise you were listening it is because the system needed those 25~50 grams... BUT in a warmer weather you would have a problem... BUT WHO CARES as in warm weather the HEAT PUMP will be out of work...
Again sorry for my LONG TEXT..
I have tried NOT to enter in any formulas or calculation because I would make it with my Greek letter formulas and then we would LOST TO TRANSLATION and more important BECAUSE I STRONGLY believ that formulas CANNOT PREDICT CAPILLARIES...
-
22-02-2010, 03:30 AM #5
Re: Capillary tube size, refrigerant, oil
With a heat-pump, there is advantage in allowing the LP rise in a controlled way. If the LP s dropped, then compressor pressure-ratio will be stretched, resulting in high compressor discharge temperatures. There is a limit as to how high the discharge temp should be allowed to climb.
As mentioned before the Tcsaturation and/or superheats, subcooling and all the book of thermodynamics can be manipulated else way. As mentioned in previous posts for R22 and R404A this can be done with Presure switches to control the fan.
Also the use of more capilaries instead of one, the quantity of refrigerant, a receiver , fan rpm, fan pitch, Diam of fan, condensing unit and many more...
What I am thinking now is that the Cap on a heat pump might and should work different since the system advantages from the HOT PLATE - not the cold.
So the more HP in the Hot plate (that in standard systems is the cold plate) the more of the benefit... So we are talking for a smaller condenser and bigger in length capillary...
Then wll need some more fluid in it, but will change the thermodynamics once more...
So you need a small receiver in order to store the excess of the refrigerant fluid.. Receiver can be a small filter of let say 60gram as the excess of refrigerant should only be a +25gr ~ 50gr.
I refer ,as have in mind an older htread of yours, to the system have in your lab and the rest of the members gave a fantastic analysis and manipulation of DANFOSS programs...
The noise you were listening it is because the system needed those 25~50 grams... BUT in a warmer weather you would have a problem...Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
22-02-2010, 09:59 PM #6
Similar Threads
-
Where can I get copper capillary tube
By hiloo in forum Air ConditioningReplies: 4Last Post: 21-06-2011, 11:04 PM -
CARE refigerants by BOC
By dogma in forum RefrigerantsReplies: 8Last Post: 23-03-2010, 12:39 PM -
capillary tube design
By Chris Zahrt in forum FundamentalsReplies: 5Last Post: 04-06-2009, 09:16 PM -
fun quiz
By Brian23 in forum New to REReplies: 6Last Post: 02-10-2007, 10:18 PM -
capillary tubes and mass flow when fed with liquid/gas
By DaBit in forum FundamentalsReplies: 15Last Post: 24-10-2002, 06:52 PM