Results 1 to 6 of 6

Hybrid View

  1. #1
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: De superheater in Air Cooled Chiller

    Desuperheater removes heat from superheated refrigerant gas after compression, but it does not remove enough heat to cause condensation of the refrigerant. The advantage is the relatively high temperature of the removed heat, the disadvantage is that the desuperheater is normally limited to 5-25% of total heat rejection.

  2. #2
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: De superheater in Air Cooled Chiller

    As NoNickName stated the purpose of the desuperheater is to remove temperature from the gas stream.

    NoNickName, nice to see you around here. How is your work progressing?
    If all else fails, ask for help.


  3. #3
    Join Date
    Oct 2007
    Location
    Nepal
    Posts
    17
    Rep Power
    0

    Re: De superheater in Air Cooled Chiller

    What is the advantage of de-superheating the hot gas when it would otherwise be cooled by air on the air cooled condenser any way especially when both heat is to be dissipated to the ambient air. I am assuming that the de-superheater would be in operation when the chiller is operated to cool.

    Quote Originally Posted by NoNickName View Post
    Desuperheater removes heat from superheated refrigerant gas after compression, but it does not remove enough heat to cause condensation of the refrigerant. The advantage is the relatively high temperature of the removed heat, the disadvantage is that the desuperheater is normally limited to 5-25% of total heat rejection.

Similar Threads

  1. Dunham Bush Chiller Alarm
    By Regulator in forum Air Conditioning
    Replies: 11
    Last Post: 08-12-2010, 01:42 AM
  2. Trane Rtaa 213 Air Cooled Liquid Chiller
    By ahamedkyana in forum Trouble Shooting
    Replies: 13
    Last Post: 08-07-2008, 10:27 AM
  3. Water Chiller
    By lana in forum Technical Speculations
    Replies: 20
    Last Post: 23-06-2007, 01:19 AM
  4. Trane Air Cooled Chiller
    By iceman007 in forum Trouble Shooting
    Replies: 26
    Last Post: 11-04-2007, 08:30 PM
  5. Mcquay PES Flooded Water Cooled Screw Chiller
    By Brian in forum Technical Speculations
    Replies: 4
    Last Post: 05-07-2006, 09:43 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •