Results 1 to 23 of 23
  1. #1
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,445
    Rep Power
    37

    Why the solinoid valve?



    Chaps had a look at a chiller yesterday

    Why have they fitted a sol valve on the eql line or am I misreading what I see?

    DSC01702.jpg



  2. #2
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    714
    Rep Power
    19

    Re: Why the solinoid valve?

    YORK YCAL O173 CHILLER UNIT, no idea why good valves though, are you aware it's an electronic expansion valve most people who first see them think they are tev's lol

  3. #3
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,120
    Rep Power
    25

    Re: Why the solinoid valve?

    It's not an equalizing line in the normal sense it's a pilot valve . I think but don't quote me on that
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  4. #4
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,471
    Rep Power
    41

    Re: Why the solinoid valve?

    when open it drives the expansion valve open, one thing to note it may be a 110v coil, being York n all. expansion valve works by applying heat to bulb of expansion valve which regulates flow, hybrid eev and tev!

    Let me know if you're ever stuck for parts, local office here is really good.

    alec
    Mostly found in the southern part of this green and pleasant land.

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Why the solinoid valve?

    Hi Richard

    It's normal for a sol valve to be fitted on the LL in chillers as this stops liquid migration to the evap during off cycles. Similar to a pump down but without the pump down if you know what I mean.

  6. #6
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Why the solinoid valve?

    its a trane chiller so trane can charge u £200 for an new alco valve.(yorks are a darker shade of brown!)

  7. #7
    TTR_Tech's Avatar
    TTR_Tech Guest

    Re: Why the solinoid valve?

    Hi Guys,

    Pretty sure that's a danfoss TGE valve or similar. Seen this done a few times before. If the solenoid valve in the equalizing line de-energized, high pressure refrigerant from the liquid inlet weeps past the pushrod, applying closing force to the diaphragm. Basically closing the TX valve via pilot. Normal superheat control is with solenoid energized. This application avoids the cost of a normal (larger) full flow solenoid valve.

  8. #8
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: Why the solinoid valve?

    Carrier used to a similar thing with a three port solenoid , forced HP liquid ontop of TXV and forcing TXV closed.

  9. #9
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,445
    Rep Power
    37

    Re: Why the solinoid valve?

    Quote Originally Posted by install monkey View Post
    its a trane chiller so trane can charge u £200 for an new alco valve.(yorks are a darker shade of brown!)
    It's been out in the sun for a few years. It is indeed York as ID'ed above..

  10. #10
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: Why the solinoid valve?

    You have to look once Richard if this line isn't connected to the HP and the valve is a small 3 way-valve? Then it's a setup like this where they use the TEV also as a SV.
    James10, I'm almost sure this is a TGE valve and surely not an EEV.

    But I don't think that refrigerant can weep across the pushrod. They're to good machined these days and they very rarely leak.Someone from Danfoss production told me this once and I posted this also here somewhere on RE (the discussion that it's better f mounting the bulb of a TEV after the equalizing line)
    Attached Images Attached Images
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  11. #11
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,445
    Rep Power
    37

    Re: Why the solinoid valve?

    Quote Originally Posted by james10 View Post
    YORK YCAL O173 CHILLER UNIT, no idea why good valves though, are you aware it's an electronic expansion valve most people who first see them think they are tev's lol

    Well it certainly fooled me. I still cannot see it.:-/

  12. #12
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,445
    Rep Power
    37

    Re: Why the solinoid valve?

    Quote Originally Posted by frank View Post
    Hi Richard

    It's normal for a sol valve to be fitted on the LL in chillers as this stops liquid migration to the evap during off cycles. Similar to a pump down but without the pump down if you know what I mean.
    I get that Frank but this sol valve isn't shutting off the LL

  13. #13
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,445
    Rep Power
    37

    Re: Why the solinoid valve?

    Quote Originally Posted by Peter_1 View Post
    You have to look once Richard if this line isn't connected to the HP and the valve is a small 3 way-valve? Then it's a setup like this where they use the TEV also as a SV.
    James10, I'm almost sure this is a TGE valve and surely not an EEV.

    But I don't think that refrigerant can weep across the pushrod. They're to good machined these days and they very rarely leak.Someone from Danfoss production told me this once and I posted this also here somewhere on RE (the discussion that it's better f mounting the bulb of a TEV after the equalizing line)

    I just had a brief visit to quote for the maintenance. I don't think it's an EEV as that wouldn't need a sol valve as it would be powered shut to give pumpdown/migration control?

  14. #14
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: Why the solinoid valve?

    Hi Richard.
    I am not convinced you looked at a YCAL (These have scroll compressors)?
    I am sure I have seen these on earlier models but cannot remember where?

    Anyway as far as I understand York use these YLLSV (Solenoid valves for several purposes).
    Some of which are :-
    So that systems can be pumped down.
    Also when the system is running and the Suction S/heat falls below 2.2c the valve will close (Coil de-energized).
    When s/heat rises above 3.3c the coil is re-energized opening the valve again.

    I think it's all to do with the low temperature running (Glycol ) options.

    Grizzly

  15. #15
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    714
    Rep Power
    19

    Re: Why the solinoid valve?

    Quote Originally Posted by r.bartlett View Post
    Well it certainly fooled me. I still cannot see it.:-/
    if you look on the underisde of the valve you'll see the electronic driver plug and in the millenium controller you can see the exv position

  16. #16
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: Why the solinoid valve?

    James10, if this is true, then it certainly interests me an I think others a lot. Can you post a link from this type of valve and controller? I was speculating for myself why this SV was inserted between the equalizing line but I will wait till I've seen your reply now.
    Last edited by Peter_1; 04-06-2011 at 07:47 AM.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  17. #17
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: Why the solinoid valve?

    There's clearly a bellow with an external bulb and if there should be somewhere a stepper or a PWM motor, then it should be mounted in the top where the bulb is located now. You can't control a Danfoss valve from the sides, only on the top.
    This is a standard TEV with a fix orifice.
    It can be that the SV is open to handle a normal SH and closed for a higher Sh, equal to the DP over the evaporator.
    Or if the line is connected to a HP point, then this is done tot use the TEV also as an adapted SV.

    Regarding this equalizing line, I will start another discussion in Fundamentals
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  18. #18
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Why the solinoid valve?

    Sorry Richard, I didn't notice that you had posted a photo....Doh!

  19. #19
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,471
    Rep Power
    41

    Re: Why the solinoid valve?

    Richard

    There is a heater attached which warms the phial on the TEV, it is a standard TEV in every other way, as posted above you can see the opening percentage on the display.

    They also as Grizzly says shut the valve on low superheat, i have a YCAL with one, haven't seen one a new machine since.

    Al
    Mostly found in the southern part of this green and pleasant land.

  20. #20
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: Why the solinoid valve?

    Hope this helps?
    Grizzly

  21. #21
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: Why the solinoid valve?

    I humble bow down my head now, plow it then as deep as an ostrich due to Grizlly's last post. I learned a lot these time. Thanks Richard and Grizzly for this.

    But then some questions arise while my head is in the sand: why they use such a valve and not a common EEV with stepper motors, PWM? What's the benefit of this?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  22. #22
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    714
    Rep Power
    19

    Re: Why the solinoid valve?

    So are we at the conclusion that this is an unconventional EXV?
    i didn't realise that it operated in the way the drawing described , nice to know

  23. #23
    TTR_Tech's Avatar
    TTR_Tech Guest

    Re: Why the solinoid valve?

    Everyone probably has it worked out, but useful info all the same...

    http://york.com.ua/files/YCAL-SB.1093518638.pdf