    I have failure message on a trane SMM Module.



    Can anyone help me with this, It is probably a communication problem. I don't have the user manual.
    The fault message that is flashing in the display is: A Com I/04.
    Please help.



  2. #2
    Join Date
    Aug 2001
    Location
    Gold Coast, Australia
    Posts
    601
    Rep Power
    28

    Re: I have failure message on a trane SMM Module.

    How many SMM modules does your chiller have?
    If it's 3 or less, ignore the message.
    It's generated because the main card is trying to communicate with card 4 and not getting a reply.
    A standard scroll chiller with 2 circuits will have a main card - the one with the display - and 2 smaller cards with a similar but square black cover & no displays. the second is circuit 2 control, and the third is the condenser fan control.
    the fourth card is just an options card, which as far as I know almost no-one in the U.K. ever specified.
    It is possible to stop the message by altering the machine configuration setting, but I'm afraid that's in the area of software only accessible to a Trane technician (or ex Trane tech. of course).
    If you don't have the 4th card, the alarm will not affect the running of the chiller & as I said earlier, can safely be ignored.
    Otherwise you'll need someone like me or a Trane technician to sort it. Ditto if you do have a fourth card.

  3. #3
    Join Date
    Aug 2006
    Location
    England
    Posts
    495
    Rep Power
    21

    Re: I have failure message on a trane SMM Module.

    hi janbanan ive emailed you smm user instructions
    Last edited by GHAZ; 30-04-2010 at 11:26 PM.

  4. #4
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    18

    Re: I have failure message on a trane SMM Module.

    Quote Originally Posted by JanBanan View Post
    Can anyone help me with this, It is probably a communication problem. I don't have the user manual.
    The fault message that is flashing in the display is: A Com I/04.
    Please help.
    Hi if u run a search in this site u will find previous posting regarding the same problem !
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

Similar Threads

  1. Carrier Transicold Container Problem
    By Shamel in forum Transport
    Replies: 39
    Last Post: 24-01-2012, 12:23 AM
  2. Trane CXAH/CGAH-240 problem
    By MortenOlsen in forum Trouble Shooting
    Replies: 7
    Last Post: 12-05-2010, 08:49 PM
  3. AEC Pinical chiller with trane comp
    By cptrdbrd in forum Commercial
    Replies: 1
    Last Post: 28-10-2009, 10:47 PM
  4. Problem with Trane RTAD100 chiller.
    By on4hf in forum Trouble Shooting
    Replies: 8
    Last Post: 14-10-2009, 09:01 PM
  5. SR2 50 models electric SBY diagonostics made simple
    By absolute-zero in forum Transport
    Replies: 5
    Last Post: 04-01-2008, 06:11 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •