    Re: earth leakage

    Can anyone advise.
    If you use a switched fuse spur or specific plugged arrangement.
    Does this then negate the need for that circuit to be on an rcd??
    I other words how specific is the term Sockets (usually interpreted as 13 amp).
    Thanks Grizzly

  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: earth leakage

    Quote Originally Posted by Grizzly View Post
    Can anyone advise.
    If you use a switched fuse spur or specific plugged arrangement.
    Does this then negate the need for that circuit to be on an rcd??
    I other words how specific is the term Sockets (usually interpreted as 13 amp).
    Thanks Grizzly
    No, switched fuse spur does not provide protection to humans or protection from fire (both of protections is main function of RCDs). It just protect outlet from overload and cable from outlet to device. It is used generally for taking power from ring main circuits usually protected by 32amp MCB and downrating the circuit protection to whatever the new circuit requires.

    Term socket usually refers to outlet for portable (that include kitchen appliances with flexible cord and plug) appliance whose power don't exceed 2000W.
    Socket rating of 13A (or 16A by VDE) is safe amount of current which ensures no overheating at connection.

    P.S. Dont blame me for possible wrong details because I did not updated these data in my head for long time.

  3. #3
    Join Date
    Apr 2007
    Location
    Lancs, UK
    Posts
    21
    Rep Power
    0

    Re: earth leakage

    Quote Originally Posted by Grizzly View Post
    Can anyone advise.
    If you use a switched fuse spur or specific plugged arrangement.
    Does this then negate the need for that circuit to be on an rcd??
    I other words how specific is the term Sockets (usually interpreted as 13 amp).
    Thanks Grizzly
    As mentioned by ecclesk

    (b) a specific labelled or otherwise suitably identified socket-outlet provoded for connection of a particular item of equipment.

    Just put a lable on it saying freezer only or air condioning only and your ok

    p.s this is with regard to the 17th ed
    Last edited by malcoa; 02-04-2008 at 09:35 AM.

Similar Threads

  1. Refrigerant Leakage
    By Pravin in forum Technical Discussions
    Replies: 11
    Last Post: 21-05-2006, 03:17 PM
  2. Earth faults
    By reggie in forum Technical Speculations
    Replies: 17
    Last Post: 28-01-2006, 06:22 PM
  3. Earth tapped transformers
    By phil68 in forum Fundamentals
    Replies: 6
    Last Post: 04-01-2006, 09:32 PM
  4. Earth continuity
    By bernard in forum Electrical
    Replies: 3
    Last Post: 04-04-2005, 06:35 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •