25-03-2008, 08:13 PM #1
Re: earth leakage
Can anyone advise.
If you use a switched fuse spur or specific plugged arrangement.
Does this then negate the need for that circuit to be on an rcd??
I other words how specific is the term Sockets (usually interpreted as 13 amp).
Thanks Grizzly
-
25-03-2008, 08:51 PM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: earth leakage
No, switched fuse spur does not provide protection to humans or protection from fire (both of protections is main function of RCDs). It just protect outlet from overload and cable from outlet to device. It is used generally for taking power from ring main circuits usually protected by 32amp MCB and downrating the circuit protection to whatever the new circuit requires.
Term socket usually refers to outlet for portable (that include kitchen appliances with flexible cord and plug) appliance whose power don't exceed 2000W.
Socket rating of 13A (or 16A by VDE) is safe amount of current which ensures no overheating at connection.
P.S. Dont blame me for possible wrong details because I did not updated these data in my head for long time.
-
02-04-2008, 09:30 AM #3
Re: earth leakage
Last edited by malcoa; 02-04-2008 at 09:35 AM.
Similar Threads
-
Refrigerant Leakage
By Pravin in forum Technical DiscussionsReplies: 11Last Post: 21-05-2006, 03:17 PM -
Earth faults
By reggie in forum Technical SpeculationsReplies: 17Last Post: 28-01-2006, 06:22 PM -
Earth tapped transformers
By phil68 in forum FundamentalsReplies: 6Last Post: 04-01-2006, 09:32 PM -
Earth continuity
By bernard in forum ElectricalReplies: 3Last Post: 04-04-2005, 06:35 PM