Results 1 to 50 of 135
Threaded View
19-08-2011, 11:15 PM #2
Re: How to assign thermodynamic properties after splitting two phase into gas and liq
Gents, to save time & make ease of reading, Jump to; # 103
Just drop the txv & sounds like flooded plate heat exchangers with low pressure vessel, chilled water system, if you plot that on a chart it will come back as you described,
(other than that I am lost for what your trying to acheive)
The liquid remains in the heat exchangers, with some in the vessel, then the boiled of vapour is piped from the top of the vessel back to compressor
You can not get much work out of the vapour compared to the liquid, transfered to vapour
What are we trying to acheive ?
R's chillermanLast edited by chillerman2006; 24-08-2011 at 06:28 PM.