    Question for an expert about Danfoss Maneurop compressor



    Hello all,

    About two weeks ago I had serviced a water cooler that uses a Danfoss Maneurop Model MT144 that uses R22 gas and 160p mineral oil.

    The water cooler has been sitting unused for 18 months, and there is no way to know when was the last maintenance and how old it is.

    As the technician opened a valve to let the gas out (to the free air ) some oil dripped from that valve and I asked if that was normal, the technician shrugged and said that yes.

    Now the water cooler seems to be working well and the temperature of the water in the pool is maintained at the correct level. There are no strange sounds and the compressor seems to be working smoothly.

    But later, I told to a friend (who works with natural gas powered refrigerators) about the oil that is apparently mixed with the gas and he said that that is the indication of an internal leak and that could be a serious problem.

    Well, as may be clear at this point I know next to nothing about those compressors and would like to know if someone out there who knows about this stuff could clear a few doubts:

    1)is the oil in the gas normal? Is that the indication of an internal, dangerous leak? why?

    2)how often should the compressor be maintained? the answers from the different people I've asked range from 6 months to 1 year.

    3)The oil and gas must be changed at the same time always? some said that only the gas must be changed.

    4)What else can I easily check to make sure that the compressor is ok?

    What else should I know about those machines (which are to me surprisingly complex)? I'm afraid that I could be easily lied to due to my ignorance.

    I've read your 101 but I think that that wasn't that helpful.

    I'll give any other information that is needed.

    Thanks in advance!



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Question for an expert about Danfoss Maneurop compressor

    Oil is moved around the system with the gas, this is quite normal.

    When you open a valve some oil may come out, also normal.

    Gas should not need changing from the day of first use unless it is removed for replacement/repair of parts.

    Check the system 6 moths/year.

    and he said that that is the indication of an internal leak and that could be a serious problem.
    This is untrue, as previously stated the oil is lightly mixed with the refrigerant and moves around the system.

    If the system is working then don't try and fix it.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Oct 2008
    Location
    Colombia
    Posts
    80
    Rep Power
    16

    Re: Question for an expert about Danfoss Maneurop compressor

    Quote Originally Posted by rolocz View Post
    water cooler that uses a Danfoss Maneurop Model MT144 that uses R22 gas and 160p mineral oil.

    ...I know next to nothing about those compressors and would like to know if someone out there who knows about this stuff could clear a few doubts...

    Thanks in advance!
    Rolocz pls find a poster and manual for MT series of Maneurop Compressor here>> http://j.mp/Blog-Josei-100406

    Saludos desde Colombia,
    Josei

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Question for an expert about Danfoss Maneurop compressor

    Unfortunately I think that OP is a one post wonder.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Jan 2010
    Location
    Bolivia
    Posts
    5
    Rep Power
    0

    Re: Question for an expert about Danfoss Maneurop compressor

    Quote Originally Posted by Brian_UK View Post
    Unfortunately I think that OP is a one post wonder.
    Hello
    Sorry for having been a "one post wonder"! Thanks for your reply, it was good for my peace of mind, but I don't agree in waiting for things to fail before taking preventive action.

    The compressor about which I originally asked in this thread is now dead. Oil was mixed with the water. The new compressor is in the way but the refrigerator technician is frowning upon the fact that the water that circulates in the circuit is full of fine sand. I fear that he may use that to avoid a warraty claim.

    The refrigerator helps in regulating the temperature of the water of a pool where concrete test specimens are left for hardening a few days. These specimens leave a fine sand that the pump pumps through the whole system, (pipes, pump, electrovalves, heater and cooler).

    There is a filter system in place but it gets saturated in about 3 days so the local maintenance technician simply removed the cartridges due to the high cost and scarce availability of the replacements. It was more important to keep the water at the right temperature. That way and with no maintenance the refrigerator worked for about 18 months after a maintenance that followed an unknown period of time being out of service.

    The refrigerator technician says that the system should only pour cool water into the pool and drain the extra water so that the "dirty" water never recirculates into the refrigerator.

    That would be very wasteful because in that city the temperature is usually above 30 celcius (86F) and the refrigerator works almost continuously except for a few weeks during winter.

    My questions is: Is there something that I can install that help remove the thermal energy off the pool water while keeping the water of the refrigerator circuit separated from the water in the pool?

    As far as I could search it looks like the only solution is a large capacity and self cleaning filter, but that is too costly, well above the budget.

    I promise that this time I will tell you about the final setup.

    Regards

  6. #6
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,920
    Rep Power
    29

    Re: Question for an expert about Danfoss Maneurop compressor

    Quote Originally Posted by rolocz View Post
    Hello

    My questions is: Is there something that I can install that help remove the thermal energy off the pool water while keeping the water of the refrigerator circuit separated from the water in the pool?

    As far as I could search it looks like the only solution is a large capacity and self cleaning filter, but that is too costly, well above the budget.

    I promise that this time I will tell you about the final setup.

    Regards
    Hi Rolocz

    the way to comabat your issue is to run two seperate water circuits through heat exchangers

    your pool water runs through one part & the chiller water runs through the other

    this way you can keep filters in the chiller circuit and leave them out of pool circuit

    sand is very abrasive so I would suggest two pumping circuits for the pool

    so one can be isolated and serviced while the other is in use

    R's chillerman
    If the World did not Suck, We would all fall off !

  7. #7
    Join Date
    Aug 2006
    Location
    england
    Age
    49
    Posts
    3,874
    Rep Power
    46

    Re: Question for an expert about Danfoss Maneurop compressor

    Have seen dairy milk filters used in similar aplications,

    http://www.milkingmachines.co.uk/uk2shop-22.htm

    They can be taken apart for regular cleaning.

    If the compressor oil has got into the water circuit the heat exchanger must be broken, if its not fixed the new compressor will fail also.
    Mostly found in Oxfordshire, UK :)

  8. #8
    Join Date
    Jan 2010
    Location
    Bolivia
    Posts
    5
    Rep Power
    0

    Re: Question for an expert about Danfoss Maneurop compressor

    Quote Originally Posted by chillerman2006 View Post
    Hi Rolocz

    the way to comabat your issue is to run two seperate water circuits through heat exchangers

    your pool water runs through one part & the chiller water runs through the other

    this way you can keep filters in the chiller circuit and leave them out of pool circuit

    sand is very abrasive so I would suggest two pumping circuits for the pool

    so one can be isolated and serviced while the other is in use

    R's chillerman

    Thanks for the answer, indeed, a heat exchanger seems to be the best alternative.

    When asked, another refrigerator technician suggested installing a heat exchanger using glycol for the refrigerator circuit.

    Seems a nice solution as it would be a simple add on and there is no need to modify electrical, electronical circuits or other parts of the system.

    Thanks for the suggestion

  9. #9
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,920
    Rep Power
    29

    Re: Question for an expert about Danfoss Maneurop compressor

    Quote Originally Posted by monkey spanners View Post
    Have seen dairy milk filters used in similar aplications,

    http://www.milkingmachines.co.uk/uk2shop-22.htm

    They can be taken apart for regular cleaning.

    If the compressor oil has got into the water circuit the heat exchanger must be broken, if its not fixed the new compressor will fail also.
    Hi Jon

    just had a look at them myself

    would suit his purpose nicely

    he could run triple bypass circuits so he can always have one clean, one in use & one being changed

    would certainly be a cheaper option than heat exchangers in the short term but I wonder how this would balance out long term, bearing in mind the abrassiveness of sand and its effect on a heat exchanger

    R's chillerman
    If the World did not Suck, We would all fall off !

  10. #10
    Join Date
    Apr 2010
    Location
    england
    Age
    51
    Posts
    297
    Rep Power
    14

    Re: Question for an expert about Danfoss Maneurop compressor

    hi CM have given this some brain time could he not fit a stainless steel heat ex to cut out the alkalie corrosion and if he fitted a settlement tank ( take pipe to a low level have section approx 3x size of running bore ) to take out or settle out small particles ie sand if it was made to be easily removed could be binned everytime it changed also as its concrete it would harden in tank at lowest point as it heavier just a thought what do you think ?
    I can fix broke but I cant fix stupid :)

  11. #11
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,920
    Rep Power
    29

    Re: Question for an expert about Danfoss Maneurop compressor

    Evening Simon

    Sounds good to me mate, any reduction in the % of sand in the mix would reduce wear/tear on the hx's

    I have seen once, a system similar to your suggestion, it was a chiller for a swimming pool in Dubia, where they were using the pool to reabilitate race horses after injury and the horses dont get out the pool to do there business

    R's chillerman
    If the World did not Suck, We would all fall off !

  12. #12
    Join Date
    Aug 2006
    Location
    england
    Age
    49
    Posts
    3,874
    Rep Power
    46

    Re: Question for an expert about Danfoss Maneurop compressor

    Make ice blocks, chuck in tank as required
    Mostly found in Oxfordshire, UK :)

  13. #13
    Join Date
    Apr 2010
    Location
    england
    Age
    51
    Posts
    297
    Rep Power
    14

    Re: Question for an expert about Danfoss Maneurop compressor

    Quote Originally Posted by monkey spanners View Post
    Make ice blocks, chuck in tank as required
    dam i knew i was missing somat
    I can fix broke but I cant fix stupid :)

  14. #14
    Join Date
    Apr 2010
    Location
    england
    Age
    51
    Posts
    297
    Rep Power
    14

    Re: Question for an expert about Danfoss Maneurop compressor

    Quote Originally Posted by chillerman2006 View Post
    Evening Simon

    Sounds good to me mate, any reduction in the % of sand in the mix would reduce wear/tear on the hx's

    I have seen once, a system similar to your suggestion, it was a chiller for a swimming pool in Dubia, where they were using the pool to reabilitate race horses after injury and the horses dont get out the pool to do there business

    R's chillerman
    the longer u made the settlement vessle the more you would remove also the lower u made it to rest of system just an idea think it would work a treat so how do i get some fractions on my board is it like super tech points an ya gotta be kudosed up to get em ? lol
    I can fix broke but I cant fix stupid :)

  15. #15
    Join Date
    Jan 2010
    Location
    Bolivia
    Posts
    5
    Rep Power
    0

    Re: Question for an expert about Danfoss Maneurop compressor

    Quote Originally Posted by chillerman2006 View Post
    Hi Jon

    just had a look at them myself

    would suit his purpose nicely

    he could run triple bypass circuits so he can always have one clean, one in use & one being changed

    would certainly be a cheaper option than heat exchangers in the short term but I wonder how this would balance out long term, bearing in mind the abrassiveness of sand and its effect on a heat exchanger

    R's chillerman


    We are leaving filtering out for now. We are adding a cleaning circuit that will have to be run maybe once a week. The valves set a circuit that pump clean water from a reservoir to drainage so the operator must push a few buttons and leave water running until it is visibly clear.

    Also, we found that the whole refrigerator system was purchased 10 years ago, but there is no way to know how long it's been working and there is no maintenance record.

    The water feels very smooth but leaves hands very dry. I was told that it isn't exactly "a very fine sand", rather puzzolane. Probably it can be rough on the surfaces when pushed by the pump. It also seems to stick and accumulate on the surfaces that are in contact with the water.

    Thanks for the assistance

  16. #16
    Join Date
    Jan 2010
    Location
    Bolivia
    Posts
    5
    Rep Power
    0

    Re: Question for an expert about Danfoss Maneurop compressor

    Quote Originally Posted by monkey spanners View Post
    Have seen dairy milk filters used in similar aplications,

    If the compressor oil has got into the water circuit the heat exchanger must be broken, if its not fixed the new compressor will fail also.
    Indeed, the heat exchanger failed and is being replaced.

    Thanks

  17. #17
    Join Date
    Apr 2006
    Location
    UK
    Age
    55
    Posts
    1,920
    Rep Power
    29

    Re: Question for an expert about Danfoss Maneurop compressor

    Quote Originally Posted by simon@parker View Post
    the longer u made the settlement vessle the more you would remove also the lower u made it to rest of system just an idea think it would work a treat so how do i get some fractions on my board is it like super tech points an ya gotta be kudosed up to get em ? lol
    The system I worked on in Dubia was using a rather huge buffer tank, water in at the middle, water out at the top, with a large gauze typr filter above the inlet to catch the straw, this allowed the horses stuff in the mix to fall to the bottom, where there was a 8inch drain valve..........as for the tech points
    Last edited by chillerman2006; 17-09-2011 at 12:18 AM.
    If the World did not Suck, We would all fall off !

  18. #18
    Join Date
    Apr 2010
    Location
    england
    Age
    51
    Posts
    297
    Rep Power
    14

    Re: Question for an expert about Danfoss Maneurop compressor

    Quote Originally Posted by rolocz View Post
    We are leaving filtering out for now. We are adding a cleaning circuit that will have to be run maybe once a week. The valves set a circuit that pump clean water from a reservoir to drainage so the operator must push a few buttons and leave water running until it is visibly clear.

    Also, we found that the whole refrigerator system was purchased 10 years ago, but there is no way to know how long it's been working and there is no maintenance record.

    The water feels very smooth but leaves hands very dry. I was told that it isn't exactly "a very fine sand", rather puzzolane. Probably it can be rough on the surfaces when pushed by the pump. It also seems to stick and accumulate on the surfaces that are in contact with the water.

    Thanks for the assistance
    the concrete will have a high level of lime in it making it very alkalie am guessing you will have a dusty atmosphere as well so water will have a high corosion rate as well will make it feel strange so would suggest you change water as much as you can to reduce the damage to chiller system if it has been in 10 yrs go fo a complete new system with a new design will be worth the outlay in long run
    I can fix broke but I cant fix stupid :)

  19. #19
    Join Date
    Mar 2011
    Location
    Australia
    Age
    43
    Posts
    67
    Rep Power
    14

    Re: Question for an expert about Danfoss Maneurop compressor

    Another option is to build a small tank, make a metal frame, line it with ply wood and then coat it with an epoxy resin fibreglass and seal it. Make a customised stainless steel cooling coil ( no fins required ) and lower it into the tank.
    Last edited by AUScooler:-); 17-09-2011 at 03:45 AM.

Similar Threads

  1. MP66 & Compressor Overheating
    By Intermez in forum Technical Discussions
    Replies: 111
    Last Post: 13-04-2010, 08:58 PM
  2. [Autocascade] Only a project ATM
    By before in forum CPU Overclockers
    Replies: 1
    Last Post: 07-05-2009, 11:13 AM
  3. Compressor Capacity
    By engrkate in forum Fundamentals
    Replies: 15
    Last Post: 13-10-2006, 12:11 AM
  4. Compressor pumping efficiency
    By shogun7 in forum Fundamentals
    Replies: 0
    Last Post: 25-02-2004, 11:50 PM
  5. noobie question re testing compressor
    By aaron cadell in forum Fundamentals
    Replies: 19
    Last Post: 28-04-2003, 08:37 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •