Thread: PHE leakage
    Feb 2012
    libya
    94
    13
    PHE leakage
    Dears,
    I use Calcium Chloride as secondary coolant for ice cream machine but the problem I face more than one time leakage on PHE so please can you advise me if there is any special treatment for Calcium Chloride solution and how can I avoid this damage
    Thanks & Regards
    3,356
    Re: PHE leakage
    Mee212,
    Can you explain where you find the leaks, is it gasket or plate damage.
    Are the plates made of titanium?
    Feb 2012
    libya
    94
    13
    Re: PHE leakage
    Dear RANGER1,
    First thank you for your reply
    the leak from plates there is no gasket and the plates made from DC04 (CS)
    Croatia
    68
    2,261
    Re: PHE leakage
    Hi, mre212
    Quote Originally Posted by mre212 View Post
    Dears,
    Thanks & Regards
    Unfortunately, there is no chemical treatment for CaCl2 to be less corrosive ... the only way is to install special heat exchanger made of titanium (quite expensive solution) and interconnecting pipes of PEH-high density polyethylene from HE to ice cream machine ...
    PEH pipes are
    • easy and light weighted
    • long living
    • low friction
    • relatively cheap
    • flexible
    • sun resistant .....
    more about here:
    http://www.engineeringtoolbox.com/pe...nce-d_329.html
    in another hand it is easy and cheap to repair your HE made of CS ....
    Hope this will help you ...
    Best regards, Josip
    3,356
    Re: PHE leakage
    mre12
    You mention no gaskets, is it a fully welded plate heat exchanger (PHE), or which type?
    Also what refrigerant are you using.
    In some cases change complete set of plates (gaskets) when you develop leak.
    Used plates could be checked over & reconditioned by PHE expert company.
    Titanium plates were difficult to get a few years ago, with 1 year wait, do not know know now though.
    josip may confirm, but also check PH level in your brine, not sure remember something as apprentice last century.
    Feb 2012
    libya
    94
    13
    Re: PHE leakage
    Thank you Guys,
    please which better to use with Calcium Chloride solution PHE made from SMO254 or Titanium
    Dear RANGER1
    we use R22 but we intend to change it by R404a