    Re: Refrigeration 101

    Quote Originally Posted by Fett View Post
    Hey Gary,

    What are the effects of excessive superheat/subcooling and lack of superheat/subcooling.

    Perhaps we can run a few example system diagnoses here.

    Example:

    Time of Day: Noon
    Type of System: Rooftop Packaged
    Outside Air Temp: 103F
    Indoor Air Temp @ Return:86F
    Indoor Air Temp @ Supply:83F
    You inspect each section of the system visually.

    Indoor Coil is clean and clear of obstruction and the air filter is new and clean.

    The Outdoor coil is slightly soiled, but nothing to be seriously concerned about.

    Outdoor Fan: Operating
    Indoor Fan: Operating
    Compressor: Operating


    Complaint: The unit is blowing warm air.



    This should be a pretty simple one... you don't need superheat or subcooling to figure it out.
    Yes... you do.

    Could be undercharge, could be restriction, could be blown valves in the compressor.

    You might think you know what the most likely problem is, but you don't really know what the problem is until you check the subcooling and the superheat.

    While you're at it, check to see what type of metering device you have.
    Last edited by Gary; 10-09-2009 at 04:11 AM.