    Quote Originally Posted by Gary View Post
    Just the opposite. High load increases SCT and low load decreases SCT... and SCT above ambient (cond TD) should remain within the 11-19K range.
    If the ambient air onto the condenser remains the same and the sct decreases with low load then the cond td must get bigger.
    If the ambient air onto the condenser remains the same and the sct increases with high load then the cond td must get smaller.

    do you mean that with a high load the cond td would be around 11k (smaller) and low load would be around 19k (larger)

    CB

  2. #2
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Refrigeration 101

    Quote Originally Posted by chillyblue View Post
    If the ambient air onto the condenser remains the same and the sct decreases with low load then the cond td must get bigger.
    If the ambient air onto the condenser remains the same and the sct increases with high load then the cond td must get smaller.

    do you mean that with a high load the cond td would be around 11k (smaller) and low load would be around 19k (larger)

    CB
    No... No... and No.

    Let's say the ambient is 25C and the SCT is 36C. The TD is 36-25=11K.

    The SCT then rises to 40C. The TD is 40-25=15K .