    Re: AWHP superheat & sub-cooling

    Quote Originally Posted by desA View Post
    The system thermodynamic balance calls for the following, at say Te,sat=12.5'C:
    1. At Tc,sat=40'C :
    Q'evap = 6.7kW
    Q'cond = 7.3kW

    2. At Tc,sat=50'C :
    Q'evap = 6.1kW
    Q'cond = 6.9kW

    3. At Tc,sat=75'C :
    Q'evap = 4.2kW
    Q'cond = 6.1kW
    Here is another set of specs that has me confused. How is any of this relevant to what we are doing?

  2. #2
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: AWHP superheat & sub-cooling

    Quote Originally Posted by Gary View Post
    Here is another set of specs that has me confused. How is any of this relevant to what we are doing?
    See the previous post, regarding appropriate initial rules/specifications (item 1).

    In this particular case, you will see that the quoted data is pegged on Te,sat & spans the Tc,sat working range.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  3. #3
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: AWHP superheat & sub-cooling

    Quote Originally Posted by desA View Post
    See the previous post, regarding appropriate initial rules/specifications (item 1).

    In this particular case, you will see that the quoted data is pegged on Te,sat & spans the Tc,sat working range.
    The quoted data depends upon a great many more variables than Te,sat and Tc,sat. First and foremost on the list would be the temperature of the liquid entering the coil.

    I'm thinking the air coil and vertical HX would do wonders for this coil.
    Last edited by Gary; 04-08-2009 at 04:18 AM.

Similar Threads

  1. 9 superheat & subcooling scenarios
    By nike123 in forum Fundamentals
    Replies: 39
    Last Post: 19-07-2011, 03:16 AM
  2. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  3. Replies: 5
    Last Post: 14-09-2009, 07:33 AM
  4. Low superheat and sucooling
    By jayaeros in forum Trouble Shooting
    Replies: 23
    Last Post: 05-07-2009, 06:21 AM
  5. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •