If this should be true, then all the refrigeration books from the last 50 years has to be rewritten.
Why an oil trap should prevent for liquid slugging? It's just the opposite: liquid can accumulate as as soon area is reduced enough, all the liquid is pushed through it at once.
And the trap on a evaporator is only for compressor startup so that oil and liquid dont effect the txv sensor
This is not worth arguing on it because both doesn't have a relation with each other.
Hi Peter1

Not liquid slugging. Slugs of oil.

Marc O'Brien showed us image 19.5 on page 455 in my RJ Dossat. I have the 3rd edition. It shows the txv bulb must be installed 30cm up the vertical riser if a trap cannot be used. If a trap can be used then the bulb can be installed before the trap on a horizontal. The trap collects oil during the off cycle so that it does not interfere with the bulb when the compressor starts.