25-05-2009, 07:41 PM #9
Re: suction line traps
Hi Peter1
Not liquid slugging. Slugs of oil.
Marc O'Brien showed us image 19.5 on page 455 in my RJ Dossat. I have the 3rd edition. It shows the txv bulb must be installed 30cm up the vertical riser if a trap cannot be used. If a trap can be used then the bulb can be installed before the trap on a horizontal. The trap collects oil during the off cycle so that it does not interfere with the bulb when the compressor starts.