    Smile Unit coolers using glycol
    Dear All,
    I need some details to my design.
    Plant : Vegetables.
    Refrigerant Ammonia
    Secondary Coolant:38% Prop. Glycol.
    The temp.for the rooms are as follows.
    Raw Goods Vegtables Mixed: 4ºC
    Cleaning & Sorting 4ºC
    Processing 15ºC
    Cleaning of dirty crates 22ºC
    Finished Goods 0ºC
    The above said are customer requirements. We cannot change.
    Basically I consider the Room temp 0ºC and take the glycol temp. as follows
    Temp in to the unit coolers: -14ºC
    Temp Out from the unit coolers:-7ºC
    My Question is
    • Is it possible to attain the room temp 22ºC in the same temperature program.
    • If not what is the solution for that.
    Hope I will get some details.
    Regards,
    TJK
    Re: Unit coolers using glycol
    My Question is
    Can you include a condenser coil in the 22°C room to provide heating?
    What is the ambient air temperature in your region? Can ambient air be used for heating?
    May 2006
    India
    82
    1,013
    Remember Relative Humidity is important. The same should be 80 to 85%.
    Mar 2007
    UAE
    43
    78
    [/font][/list]Can you include a condenser coil in the 22°C room to provide heating?
    Ambient Temp:53 C
    The Condenser Coil is placed outside of the cold room only.ambient air be cannot be used for heating.Because The ambieent temp & RH are varying suddenly
    Our Area Is UAE
    Rgds,
    TJK
  1. Replies: 12
  2. SL/SB-400 Pump Down Procedures
    By absolute-zero in forum Transport
    Last Post: 29-01-2008, 09:27 PM
  3. Thermo King OptiSet
    By REEFER-TEK in forum Transport
    Last Post: 06-12-2007, 07:23 PM
  4. TK basic micro-p features and functions
    Last Post: 05-12-2007, 06:25 PM
  5. Brands unit coolers USA?
    By Friobernal in forum Technical Discussions
    Last Post: 06-08-2003, 08:35 PM