    Humidity Too High



    HI everyone, I have an evaporator coil of a cooling tower wich is for a 1200 square feet area . The humidity inside is about 80% so I would like to decrease it . The customer used a humidifier inside the cooling place ,he got about 1 gallon of water every single day . He doesn't want to change the size of the unit.
    Can somebody help me on this ,please?



  2. #2
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    330
    Rep Power
    17

    Re: Humidity Too High

    Quote Originally Posted by tijojo View Post
    HI everyone, I have an evaporator coil of a cooling tower wich is for a 1200 square feet area . The humidity inside is about 80% so I would like to decrease it . The customer used a humidifier inside the cooling place ,he got about 1 gallon of water every single day . He doesn't want to change the size of the unit.
    Can somebody help me on this ,please?
    I'm not sure what you are referring to when you state "evaporator coil of a cooling tower"........a chiiled water evap maybe? Can you give us more information on the actual equipment you have along with temperatures.

    And I suppose you meant de-humidifier.

    The way to decrease the humidity in a cooler with conventional refrigeration is to increase the evap TD which relates to using a smaller evap...which will lower the SST... which will decrease the capacity..........or if it is a chilled water system, increase the water flow to increase the btuh capacity which will increase the evap TD.

    There aint no magic.

    Let us know what you have.

  3. #3
    Join Date
    Sep 2006
    Location
    Miami
    Age
    48
    Posts
    5
    Rep Power
    0

    Re: Humidity Too High

    Thank You . It Is A Chiller Water System . I Thank My Company Increased The Evaporator Coil. May Be That's Why We Get That Problem.
    What Do You Think?
    Last edited by tijojo; 07-03-2008 at 05:41 AM.

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: Humidity Too High

    Quote Originally Posted by tijojo View Post
    Thank You . It Is A Chiller Water System . I Thank My Company Increased The Evaporator Coil. May Be That's Why We Get That Problem.
    What Do You Think?
    I don't think that you have provided enough information for anybody to reach any sensible conclusion.

    Water flow rates, water temperatures, air temperatues etc.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Humidity Too High

    I don't mean to be offensive, but at this point, you don't seem to know enough about refrigeration to be able to properly describe the system you are working on, or to ask questions that make sense.

  6. #6
    Join Date
    Feb 2008
    Location
    India
    Age
    43
    Posts
    28
    Rep Power
    0

    Re: Humidity Too High

    Quote Originally Posted by tijojo View Post
    Thank You . It Is A Chiller Water System . I Thank My Company Increased The Evaporator Coil. May Be That's Why We Get That Problem.
    What Do You Think?
    Hi

    if in simple words you want to decrease RH level inside the conditioned space.
    *airflow reduction will help if you have modulating type blower/fan.
    *Increase in return air temperature will also reduce RH level.1 deg increase will result in 3-5% RH drop.
    *Give moisture barrier treatment to the room walls.
    *Make sure room is Air tight with no air exchange.
    *decrease inlet chilled water temperature.
    * check for the room heat load if heat load is less than the design RH level would increase.

    let me know again.

    Regards
    Praveen

  7. #7
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Humidity Too High

    What it comes down to is supply air wetbulb temperature, which if measured close to the coil is almost identical to drybulb temperature. In order to maintain 50% RH, this temperature needs to be about 20F/11K lower than the room temperature. The supply air temperature can be regulated by chilled water temperature and/or blower speed.

Similar Threads

  1. High Efficiency Mini Split for High Humidity Area
    By Joybob in forum Air Conditioning
    Replies: 27
    Last Post: 07-04-2008, 11:06 PM
  2. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  3. High humidity in cold room
    By nimamu in forum Technical Speculations
    Replies: 20
    Last Post: 07-01-2008, 04:02 PM
  4. High Humidity Chamber
    By smpsmp45 in forum NH3
    Replies: 7
    Last Post: 12-09-2007, 07:25 AM
  5. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •