Thread: Friga Bohn correction factors
-
18-08-2006, 09:24 PM #1
Friga Bohn correction factors
Does any one have the correction factors for a Friga Bohn MUC420 using R134a gas evaporating at -6oC as the book only shows R404a, I need to check the duty on one I fitted earlier today, not convinced it is matched to the existing condensing unit.
-
19-08-2006, 08:33 AM #2
Friga Bohn Correction =0.905
IS this usefull?
It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
19-08-2006, 01:22 PM #3
Re: Friga Bohn correction factors
Dear Andy W,
The literature of MUC does not intimate any thing about the application range of 134a. However if you can intimate to me the capacity of the unit required and the condensing temp as you have already intimated the required temperature and the model, I may assist you to get the rated capacity with R 134a. I presume that the room temperature will be 0 Deg. C. If otherwise, please intimate the Room temperature.
With best wishes, Samarjit SenLast edited by Samarjit Sen; 19-08-2006 at 01:33 PM.
-
19-08-2006, 02:12 PM #4
Re: Friga Bohn correction factors
Dear Andy W,
The correction factor for 134a from R 404a as per Friga Bohn is 0.91. If you want further details or the pdf documents on this and the MUC series please contact me and let me know as to how can I attach the relevant documents. I am not much of an expert on computer operating.
-
19-08-2006, 02:22 PM #5
Re: Friga Bohn correction factors
Andy W,
Pls. find the relevant document. I hope this serves your purpose.
-
19-08-2006, 04:56 PM #6
Re: Friga Bohn correction factors
As already stated in the header of post 2 Samarjit Sen
May I ask, why you named the document Evapo.gb.pdf?
I ask you this because Evapo Belgium was long time the sole importer of Friga Bohn since ECR bought Evapo and they were integrated in the European ECR group.Last edited by Peter_1; 19-08-2006 at 04:58 PM.
It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
19-08-2006, 05:51 PM #7
Re: Friga Bohn correction factors
Hi Peter 1,
This is the name given in the Friga Bohn documents. If the documents serves the requirement then why bother about the name.
With best wishes, Samarjit Sen
-
19-08-2006, 06:15 PM #8
Re: Friga Bohn correction factors
Thanks guys, exactly what I was after, what would I do with out you all.
-
19-08-2006, 06:38 PM #9
Re: Friga Bohn correction factors
Originally Posted by Samarjit Sen
That's all, especially because I first met BESC5240 at Evapo
Nostalgic feeling, you know S.S.It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
19-08-2006, 06:45 PM #10
Re: Friga Bohn correction factors
Sorry Peter 1 if I have offended you which I did not mean to be. I shall find out why it has been named as such from Heatcraft as they are now dealing with Friga Bohn products.
With best wishes, Samarjit Sen
-
19-08-2006, 07:36 PM #11
Re: Friga Bohn correction factors
Originally Posted by Samarjit SenIt's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
14-02-2008, 10:24 AM #12
-
14-02-2008, 05:55 PM #13
Re: Friga Bohn correction factors
It is minus 6 Deg. C. Further with R 134a you cannot get minus 60 C.
-
15-02-2008, 09:15 PM #14
Re: Friga Bohn correction factors
I find the capacity tables of evaporators in general to be very optimistic. I have got the impression that the capacity is measured in a dry environment, and then multiplied with 1,25 to simulate humid condition. However, how moist have it got to be in a cold rom for the evaporator capasity to get 25% higher?!? 150% humidity? I have learned to multiply the wanted evaporator capacity with at least 1,5 and then pick the right evaporator. And i can adjust the XV.
-
15-02-2008, 09:30 PM #15
Re: Friga Bohn correction factors
Hello andy bitzer uk have cd disks on friga bohn products with calculations on it , because i got one this week.
-
15-02-2008, 09:45 PM #16
Re: Friga Bohn correction factors
That's an obligation of the certification organisation Eurovent, otherwise you compare apples with pears.
The capacity of evaporators in the brochures is always less then a real life situation.
Same for compressors, they're given with O°K subcooling, so capacity is less then a real life situation where you have some degrees of SC.It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
15-02-2008, 11:37 PM #17
Re: Friga Bohn correction factors
-
16-02-2008, 09:56 AM #18
Re: Friga Bohn correction factors
Well, I have then another question I will throw into this thread: if you read an evaporator capacity in the catalogue or the software gives you one, do you have to subtract additionally from this given capacity the power of the fan motors?
It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
16-02-2008, 10:58 AM #19
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Friga Bohn correction factors
Last edited by nike123; 16-02-2008 at 11:05 AM.
-
16-02-2008, 11:07 AM #20
Re: Friga Bohn correction factors
No. This capacity should be the "register" capacity, same as compressor/unit capacity - loss in suctionline. Heat from the evaporator motors is no different from other heat loads. Meaning you have to add the eveporator motors when you calculate the total heat load from lights transmission, products and so on, on the evaporator
-
16-02-2008, 02:23 PM #21
Re: Friga Bohn correction factors
It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
16-02-2008, 03:05 PM #22
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
18-02-2008, 01:56 PM #23
Re: Friga Bohn correction factors
When you are assesing the Heat Load of the Room, the fan motor load has to be considered, In most of the software you will find that there is motor load. Once you assess the heat load which also includes tha fan motor load, you select an evaporator suitable for your application and based on the heat load. While selecting the Evaporator, there are factors like fin spacing, Td, and of course the refrigerant and the Te has to be provided. FrigaBohn has a very good software and so has the Helpman. Even Kuebas software is good. The software gives us a general idea and based on this we have to utillise our experience and knowledge to get a suitable Evaporator.