    Daikin split problem (any ideas)



    Hi I was wondering if anyone could help with a problem i encountered today with a daikin split system.When the compressor starts both suction and liquid lines pump down to 0 psi.Both valves are open and no problem with a shortage of gas.Any ideas would be greatly appreciated,
    Thanks John



  2. #2
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: Daikin split problem (any ideas)

    If the system was running in cooling then might be blockage at outdoor unit liquid line expansion device.
    The compressor pumps all refrigerant into the outdoor coil which just fills up with the liquid but it cant get out down the liquid line to the indoor unit.

  3. #3
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Daikin split problem (any ideas)

    It sounds like its pumping its self down, a blockage in the liquid line.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  4. #4
    julian E's Avatar
    julian E Guest

    Re: Daikin split problem (any ideas)

    Hi ya john i had this fault on a daikin unit on monday and found it to be the EXV if you turn the power off to the condensor and turn it back on is the expansion device noise because thats how i found my fault.
    good luck julian

  5. #5
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Daikin split problem (any ideas)

    John,

    When you say liquid line, have you connected to the smaller valve on the outside of the unit?
    If so, then both your gauges are connected on the suction side of the expansion device.
    Depending on the model you're looking at, I would say that either TEV, Capillary tube, drier or strainer is blocked (or in the case of TEV-faulty).
    If this is a heatpump, it would be interesting to know what happens in heating mode.

    good luck

  6. #6
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: Daikin split problem (any ideas)

    Check to see if the electronic TX is plugged in properly.
    When powering up you'll hear the valve hammer away seating itself (though it might only be a slight rumble so you'll have to listen closely).
    Make sure the valve coil is properly secured to the vavlve body too.
    If it's plugged in, seated properly, and does the start up rumble/hammer, then you have a blockage in the liquid line somewhere. Maybe at the valve itself, but it could be at the strainer or anywhere on the liquid line.
    Does this unit have a condenser gauge schrader port inside the unit anywhere?

  7. #7
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,667
    Rep Power
    51

    Re: Daikin split problem (any ideas)

    Quote Originally Posted by airconjohn View Post
    Hi I was wondering if anyone could help with a problem i encountered today with a daikin split system.When the compressor starts both suction and liquid lines pump down to 0 psi.Both valves are open and no problem with a shortage of gas.Any ideas would be greatly appreciated,
    Thanks John
    How did you determine this?

  8. #8
    Join Date
    Oct 2006
    Location
    UK
    Age
    57
    Posts
    165
    Rep Power
    18

    Re: Daikin split problem (any ideas)

    Do you have a model number?

  9. #9
    Join Date
    Oct 2007
    Location
    jersey channel islands
    Posts
    186
    Rep Power
    19

    Re: Daikin split problem (any ideas)

    hi, if you find all valves to be working as should be and this unit uses quarter pipe work , it may be worth reclaiming all the gas and testing for a blockage in the pipe work , i have seen quarter blocked with too much braze.
    if you cant find any joins dissconect the pipe workat the outdoor and put some o f n thru the quarterand see if you can hear it coming back thru your suction pipe , particularly if you did not do the install yourself.
    hope this is of help to you.
    there are very good people on this site, you are bound to get the answer you need..

  10. #10
    Join Date
    Nov 2007
    Location
    newcastle
    Age
    51
    Posts
    17
    Rep Power
    0

    Smile Re: Daikin split problem (any ideas)

    Quote Originally Posted by airconjohn View Post
    Hi I was wondering if anyone could help with a problem i encountered today with a daikin split system.When the compressor starts both suction and liquid lines pump down to 0 psi.Both valves are open and no problem with a shortage of gas.Any ideas would be greatly appreciated,
    Thanks John
    hi there if no blocked pipes 3 way valve ? if in doubt give it a .just a thought

  11. #11
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,667
    Rep Power
    51

    Re: Daikin split problem (any ideas)

    Quote Originally Posted by airconjohn View Post
    Hi I was wondering if anyone could help with a problem i encountered today with a daikin split system.When the compressor starts both suction and liquid lines pump down to 0 psi.Both valves are open and no problem with a shortage of gas.Any ideas would be greatly appreciated,
    Thanks John
    Any response airconjohn? - are you still with us?

  12. #12
    Join Date
    Dec 2007
    Location
    England
    Age
    83
    Posts
    74
    Rep Power
    17

    Re: Daikin split problem (any ideas)

    Hello is there any body there ( wherefore art though) airconjohn if you do decide to return my bet is on, (Still Learning).now i am new to this site many ego,s are on hold with regards to who comes up with answer to your immediate problem. Grump

  13. #13
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Daikin split problem (any ideas)

    Another one hit wonder
    The difference between genius and stupidity is that genius has its limits.

    Marc

  14. #14
    Join Date
    Oct 2007
    Location
    Midlands
    Age
    51
    Posts
    21
    Rep Power
    0

    Re: Daikin split problem (any ideas)

    where has airconjon......Gone?

  15. #15
    Join Date
    Nov 2006
    Location
    Scotland
    Age
    43
    Posts
    85
    Rep Power
    18

    Re: Daikin split problem (any ideas)

    Ha ha ha!Nice one!I think everyoe confused airconjohn,he must have hit the road...No offence airconjohn...

Similar Threads

  1. Daikin twin split
    By Lippygit in forum Trouble Shooting
    Replies: 2
    Last Post: 28-07-2007, 06:28 PM
  2. !!big Daikin Problem!! Codes,u4,pj, And E0
    By airconengineer in forum Air Conditioning
    Replies: 21
    Last Post: 31-05-2007, 09:04 PM
  3. Daikin FH series problem
    By pdingle in forum Air Conditioning
    Replies: 7
    Last Post: 13-08-2006, 06:45 PM
  4. Daikin problem
    By Jambo in forum Trouble Shooting
    Replies: 4
    Last Post: 28-07-2006, 07:42 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •