    Hi
    Thanks for this forum i solve many problems with your help.
    I now that with your experience you can help me with this question.
    I'm working on "Daikin" model RYP125L7W1(duct and cassette unit ) and RZQ200C7Y1B (VRV system)
    distance between indoor and outdoor unit is width-10m, height-10m (indoor units are heigher) I don't have problem with AC but can this distance be a problem in the future, and how can i calculate addition R407.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: distance

    Additional refrigerant ? The installation instructions should give you the extra weight of refrigerant to add if required.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Jun 2005
    Location
    California
    Posts
    394
    Rep Power
    19

    Re: distance

    You may want to do the sub cooling method if you have TXV or superheat method with fixed orafice if you can't get mfg data

  4. #4
    Join Date
    Jan 2008
    Location
    England
    Posts
    10
    Rep Power
    0

    Re: distance

    10 metres between indoor and outdoor? you shouldnt need any additional refrigerant. and you say vrv but only mention 1 indoor unit. if its only a split, daikins precharged refrigerant amount is in the manual or on condenser cover. my first reply, hope it helps.

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: distance

    When you work with vrv/vrf systems in general, you need to calculate amount of add-on refrigerant no matter if pipes are 2m or 100m long because they are not pre-charged for some length. You need instalation manual and then calculate these amounts based at actual lengths of all branches and main pipes in system.

  6. #6
    Join Date
    Sep 2007
    Location
    IL
    Age
    47
    Posts
    56
    Rep Power
    17

    Re: distance

    First of all, both of the mentioned units are outdoor Sky Air units (not VRV).
    Second, RZQ uses R-410 (and not R-407).
    Third, up to 30 meters (in RZQ200) no additional refrigerant is required. For longer distances you should use the installation manual.

Similar Threads

  1. refrigeration unit cooling capacity
    By nestor_greg1220 in forum Technical Speculations
    Replies: 8
    Last Post: 05-09-2007, 02:10 PM
  2. distance learning for NVQ2
    By LRAC in forum Training
    Replies: 4
    Last Post: 20-05-2007, 10:43 AM
  3. Distance Learning
    By harsen in forum Training
    Replies: 2
    Last Post: 11-03-2007, 11:36 AM
  4. Does distance affect capacity?
    By Dimitris in forum Technical Discussions
    Replies: 5
    Last Post: 12-03-2006, 02:49 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •