    Re: Superheat

    Quote Originally Posted by nike123 View Post
    I just have sensed sudden urge to color this statement in red, because I think that is most important thing that someone need to check before any other action on RAC system.
    Indeed, if I were teaching a course on system trouble shooting, I would not allow my students to use gauges until somewhere near the end of the course.

    They would become airflow experts first.

    They would be taught how to measure saturation temperatures without gauges.

    And then they would be taught to measure saturation temperatures with gauges.

    And heaven help the student who tells me what the pressures are. I want to know what the saturation temperatures are. Trouble shooting is about temperatures, not pressures.
    Last edited by Gary; 21-01-2008 at 06:20 PM.

Similar Threads

  1. TXV Superheat
    By Gary in forum Trouble Shooting
    Replies: 15
    Last Post: 24-04-2011, 02:51 PM
  2. Carrier 23xl chiller-Low discharge superheat alarms
    By Bradysmill in forum Trouble Shooting
    Replies: 7
    Last Post: 25-04-2010, 07:43 PM
  3. TEV superheat setting and low temperatures
    By DaBit in forum Fundamentals
    Replies: 11
    Last Post: 01-03-2010, 02:11 AM
  4. Superheat debate
    By zolar1 in forum Technical Discussions
    Replies: 5
    Last Post: 08-02-2008, 09:57 PM
  5. Superheat
    By shogun7 in forum Fundamentals
    Replies: 24
    Last Post: 23-08-2004, 05:54 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •