Results 1 to 32 of 32
Thread: R12 vs R134A
    Perth, Australia
    87
    R12 vs R134A
    One of the differences between auto air conditioners that have been redesigned from R12 to R134a is that the condensers have gone from serpentine to pseudo-parallel.
    What is the refrigerant property involved that has caused this?
    Mark Baker
    Mark Baker
    Mar 2002
    Sydney Australia :D
    47
    Question
    Dont think that the refrigerant properties has much to do with the design. It is possibly just a more efficient coil.
    134a is a direct replacement for R12 just enviromentally friendly.
    Yes/no??
    Jan 2002
    Mirfield
    32
    no its not, there is a reason, r134a isnt as efficient.
    j p g
    Mar 2002
    Sydney Australia :D
    47
    It may not be as efficient......but Check your stuff Brian R134a is a replacement for R12 in the automotive industry....
    :cool: Do the job once & do it right. :cool:
    Jun 2001
    N.Ireland
    1,630
    I was at a meeting today where the phase out of R134a was discussed, in relation to auto A/C. Favoured replacement seemed to be R744 (co2)
    Regards. Andy.
    Apr 2001
    2,099
    27
    All I know most techs detest R134a
    It is a weird gas and is definately not as efficient as our darling old R12
    Filters and cap tubes blocking up, compressors suffering from premature failure are being blamed on R134a
    How true this is I dont know
    Me I steer clear of R134a unless I cannot help it
    I prefer Isceon R49 instead
    St. Louis, MO
    509
    You might be amused to know that Isceon 49, aka R-413A, is 88 percent R-134a by weight...
    Prof Sporlan
    St. Louis, MO
    509
    It'll be interesting to see if Mercedes, et al, can make these systems work well. The biggest drawback with these system will be the fact they will likely cost quite a bit more than comparable R-134a systems.
    Prof Sporlan
    Apr 2001
    2,099
    27
    Ahh Prof, why do you have to spoil the party ???
    Everytime I look at a bottle of R49 now, I will see that dastardly evil R134 lurking and smirking inside!!!
    Jan 2003
    East Anglia
    1,160
    I am sure R134 was developed as a bad joke by somebody.
    every time you have a compressor failure you know there is a good chance the capilary tubes will be blocked. I have heard some people refer to R404 as mr leaky but this must run a close second. Also (Winge-winge) could somebody make a leak checker that can actually pick it up. I know although it shouldn't directly replace r12 (Dif oils ect) i have seen a lot of OLD !!!!!!!! freezers that were R12 have R134 put in them and seem to work ok.
    My motto, If its an R12 Unit and not working SCRAP IT. I know this isnt enviormentally friendly with the fidge mountains everywhere and doesn't bring in revenue to the service dept but how many of you if your'e fridge broke down at home if on R12 would spend time & money trying to repair it.
    St. Louis, MO
    509
    His name was Albert Henne, and he synthesized R-134a in 1936, 5 years after R-12 was introduced. He worked with Thomas Midgely of General Motors who is credited with developing R-12 in 1931.
    Prof Sporlan
    May 2002
    The Netherlands
    48
    274
    I read a technical article about it, and the results of the CO2 airco were very good, compared to a same sized R134a one. Construction is a bit different; they call the condenser a 'gas cooler', and condensation is done by heat exchange between the cooled gas and the suction from the evaporator.
    Still, pressures are high, and connections tough (CO2 tends to dissolve plastics and elastomers, so steel gaskets are used.)
    But it sure is an interesting technology.
    St. Louis, MO
    509
    This is characteristic of any trans-critical refrigeration cycle. Since "condensing" temperature is above critical, you getting any real condensation from your air cooled condenser coil becomes problematic. As a result, it becomes a discharge gas cooler. A suction/cooled gas heat exchanger becomes necessary to condense the gas.
    Prof Sporlan
    May 2002
    The Netherlands
    48
    274
    What they failed to mention in the article was how the system would start up at high ambient temperatures. You need cold from the evaporator to condense the CO2, which is not available at startup.
    Pressures are ridiculous. 35 bar evaporating and 100+ bar discharge.
    St. Louis, MO
    509
    You'll generate some cooling going from high pressure gas/two-phase to low pressure, albeit much less than with high pressure liquid. One would think this would adversely affect pulldown. Also, it would make expansion device sizing a bit more interesting...
    Prof Sporlan
    Jun 2001
    N.Ireland
    1,630
    so how do you condense the vapour on the high side
    using the evaportor on the low side?? can't see that, a condenser THR is the evaporator capacity+the absorbed power.
    Is there another fridhe system cooling the R744 in the condenser
    Regards. Andy
    Jan 2003
    Crewe, United Kingdom
    58
    723
    22
    I guess that the REAL R+D on this type of system is how to make the pipework corrode just out of warranty! R134a just wouldn't be a problem if the car manufacturers used better quality alloy or even copper. If I was cynical I would say that using a mild steel clip to retain an alloy pipe in an area that would collect salt water is a good way of ensuring that you can sell a similarly constructed replacement for £70, plus labour plus recharging the system (Some main agents charge the system twice, once to find the leak and then to charge the system)
    Karl
    Mar 2002
    Sydney Australia :D
    47
    I think Karl Has just hit the nail on the head people.
    After all how long has is taken them to produce bodywork that doesn't rust...
    May 2002
    The Netherlands
    48
    274
    Originally posted by Andy
    [B]Hi
    Something like that. What they do is the following: they drive high side pressure up quite a bit. This releases very hot gas (the article spoke of 150C), which is cooled (maybe desuperheated is a better term) in the 'gas cooler'; our former condenser. However, since the temperature of the gas cooler is likely to exceed 32C (CO2 critical temp), the gas won't condense over there.
    Then, in the heat exchanger between suction and cooled gas (normally our liquid line), the temperature of the CO2 drops below 32C, allowing it to condense to liquid. The energy released by this process heats the suction gas, and appears at the discharge after compression, where the gas cooler can get rid of it.
    A phase separator catches off the liquid CO2, and feeds it through an expansion valve.
    Thus, when the system is running, condensing the CO2 is not a problem.
    Only startup of such a system at ambients above 32C seems problematic to me. They didn't mention how they solved it.
    Jun 2001
    N.Ireland
    1,630
    Hi Dabit
    thank you for the explaination
    Would the pressure also drop below the critical point to allow condensation to take place
    Regards. Andy
    May 2002
    The Netherlands
    48
    274
    I am not sure what you mean. When a gas is cooled below it's critical temperature , and a pressure is maintained above it's equivalent saturated pressure, then it will condense, right?
    Or am I missing something?
    Jun 2001
    N.Ireland
    1,630
    Hi Dabit
    maybe I am, not you
    my thinking is by lowering the pressure below the critical point normal condensation occurs, as in any vapour cycle.
    If condensation was able to take place without a drop in pressure why not just use the gas cooler to condense the vapour, or is there a problem of the air not being low enough
    Regards. Andy
  23. #23
    May 2002
    The Netherlands
    48
    274
    I think you are failing on the critical pressure.
    Mind you, the 'critical pressure' is the saturated pressure of the refrigerant at the 'critical temperature'.
    Above the critical temperature the refrigerant cannot condense anymore, but for pressure there is not such a law.
    But again, I might be wrong.
    The critical temperature also prevents the CO2 from liquefying, since the gas cooler is likely to be warmer than 32C if ambient gets above 25C or so.
  24. #24
    Jan 2003
    58
    723
    22
    Stuart, they've known for years how to make bodywork that doesn't rust, they've just come up with a better money spinner. Offer a five year bodywork perforation guarantee (Provided your main agent inspects it every year at your cost) and hammer you on luxury item parts such as air con components and the like. Ha! I've even scrapped a brand new,genuine, still in the box condenser for a Renault Laguna because of corrosion, what chance do motorists have?
    Where as R134a has been adopted as the replacement for R12 it is not a drop in and does not mix well with mineral oil so when replacing R12 the lubricant should be changed, which is easier said than done. In the UK I would doubt that anyone could tell the difference between R12 and R134a in their a/c system, but those colonials, especialy those in Arizona and Texas prefer to use a parallel flow condenser with R134a
    Karl
  25. #25
    Mar 2002
    Sydney Australia :D
    47
    Smile
    Again Karl
    Quite true I agree with everything there..
    the layman will not know any difference between the two gasses
    As long as the a/c works when it is turned on then they will be quite happy.
    And why not because as long as it is in the system it doesn't cause anyone a problem....
    Its when it escapes it becomes the problem we all know & detest so much.
  26. #26
    Mar 2002
    Sydney Australia :D
    47
    By the way: Its isn't necessary to remove the oil from the R12 system according to the manufacturers.
    Details: www.efproducts.com
    Although a compatable oil is recomended.
  27. #27
    Sep 2003
    Seychelles
    I am happy to observe such discussion regarding R134a. From experience this refrigerant has brought more problems to the domestic appliances. Filter blockage is quite common and if care is not taken when recharging there is also the problem of overheating and eventual compressor failure. How do you think of the use of 'Hydrocarbon' as a direct drop-in gas? Had any experience?
  28. #28
    Jan 2003
    58
    723
    22
    Stuart, these are what the guys over the pond call "Death kits" In the temperatures that you find in the UK adding an ammount of PAG or Polyolester on top of the mineral oil works, it's not right but it works. In the US you can lose too much due to the system having too much oil in it. Did you notice the absence of every Fridge and a/c engineers first rule? (No not the one that says "Dont get caught") Nowhere in the instructions did they mention a Vacuum!!! and that is where things get expensive.
    I've run tests on that Leak Sealer also and that is C##P too
    Karl
  29. #29
    Aug 2001
    1,046
    An interesting observation, Prof.
    As well as chemicals for refrigeration at DuPont, Midgeley and his associates were, I believe, working with General Motors in the early 1920s on the addition of tetraethyl lead to petroleum fuel to improve its performance and to avoid premature engine damage.
    A double Whammy, perhaps?
    ________
    trichome
  30. #30
    KoBushi's Avatar
    KoBushi Guest
    Re: R12 vs R134A
    I haven't seen anyone mention R414B aka HotShot.
    It is a drop-in replacement for R12 (unlike 134a) and is more efficient than original R12
    I'll never use R134a again so long as HotShot is still available.
  31. #31
    Jan 2003
    58
    723
    22
    Re: R12 vs R134A
    Surly in North Carolina R12 is still available. We found that R22 in HotShot caused the flexible hoses to decompose, but whatever
    Karl
  32. #32
    Jun 2004
    Finland
    136
    Re: R12 vs R134A
    Wow! I didn't know R12 is still available especially in USA . I thought EPA is controlling these things with hard hand?
    Anyway, according to my experience the real drop-in replacement for R12 based car a/c is Isceon 49. Excellent stuff. Regardelss of Thermo King being using Isceon 69L (R403b) as a replacement for old R502 systems, TK doesn't recommend Isceon 49 as a replacement for their R12 systems. IIRC something to do with the oil circulation.
  1. R507 in an R134a compressor: any danger?
    Last Post: 21-12-2009, 12:44 AM
  2. R12 to R134a
    By fireblade in forum Domestic
    Last Post: 19-08-2006, 09:02 PM
  3. Pressure Transmitter R134a Setpoints
    By cooltrain in forum Technical Speculations
    Last Post: 28-02-2005, 09:05 AM
  4. Replies: 5
    Last Post: 01-03-2004, 09:59 PM
  5. R507 in an R134a compressor: system design
    Last Post: 01-05-2003, 09:25 AM