    Tom Richardson,

    In re: to superheat, read this:

    http://www.hvacwebtech.com/trouble.htm

    or this:

    http://www.refimax.com/docs/therm_exp_valve.htm



    Measure your suction line temperature exiting the evaporator (or cold plate).

    Measure your suction pressure.

    Refer to the "satuaration" temperature of your pressure reading on your pressure/temperature chart.

    Subtract your saturation temperature of the refrigerant pressure (chart temperature reading) from your suction line temperature and the result is the superheat (the degrees above the boiling point that the refrigerant is at as it leaves the heat exchange device, evaporator or cold plate).

    For medium temp, typically you want to be at about 7-9degrees, but in your close-coupled system a little bit more is not bad. You can adjust the responsiveness of your cold control scenario by relocated the cold control sensing location. For more positive reaction (defrost) you would locate the sensing location closer to the inlet of the evaporator.
    Last edited by herefishy; 28-06-2003 at 10:20 PM.

Similar Threads

  1. Leaking frost free fridge-freezer
    By diment01 in forum Domestic
    Replies: 5
    Last Post: 22-06-2006, 11:49 PM
  2. Frost Project
    By JimmyMurphy in forum Domestic
    Replies: 1
    Last Post: 10-06-2006, 06:00 AM
  3. frost on compressor pipes
    By gabyz in forum Domestic
    Replies: 4
    Last Post: 17-05-2006, 05:09 AM
  4. distributor frost
    By Lc_shi in forum Fundamentals
    Replies: 1
    Last Post: 04-03-2006, 08:12 AM
  5. frost free's the death knell!!
    By billyfridge in forum Domestic
    Replies: 5
    Last Post: 20-06-2005, 10:58 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •