Thread: overhaul
-
14-08-2007, 04:17 AM #1
overhaul
please give me suggest, may I use compressor more than 5000 hour for the first time, my NH3 compressor is a reciprocating compressor, two stage, Sabroe 116
-
14-08-2007, 04:48 AM #2
Re: overhaul
It would be best to use the Sabroe guidelines for replacement intervals. Remember, these operating hours are recommended average hours. A compressor that is treated badly may require more frequent inspection and replacement of parts. This is only something you can decide.
I have seen compressors that are treated well and never been taken apart also.If all else fails, ask for help.
-
15-12-2007, 07:32 PM #3
Re: overhaul
you are recommend to perform minimum check/s.
these days, QC for compressor before delivery is on random basis.
you wouldn't know if you are to 'choosen' one with defective parts.
it is good to check & change the lube oil; moreover some manufacturer place some cloth type filter at the strainer. if you do not check, ....
perform the isnpection if you trust onyl what you see.
-
16-12-2007, 07:01 PM #4
-
25-01-2008, 08:22 PM #5
Re: overhaul
I would say 10,000Hrs seems to be the rule of thumb with Recip. The diminishing factor to these hours is the Stop Start
-
25-01-2008, 09:53 PM #6
-
25-01-2008, 10:31 PM #7