    R134 refrigeration systems




    Hi everybody,
    This one's reg R134a systems used in freezers.
    I wish to know how low one can go suction pressure. If the suction pressure is too low, it may cause leakage of out-side air in to the system. But if one is working for cabinet temp of say (-) 30°C, the suction pressure has to be quite low. Can some-one enlighten me how low (suction pressure ) is safe over long term ??



  2. #2
    Join Date
    Feb 2005
    Location
    Hong Kong
    Posts
    190
    Rep Power
    20

    Re: R134 refrigeration systems

    Hi there UMAKANTVH, marhabba, shlonek!
    Presumably you are talking of regular 1 stage vapour compression system as you posted under 'domestic'.

    For not alone reasons of the vaccum condition but also summing up as 'practical and efficiency' reasons you would not, could not use 134a for low temp freezer where you desire a cabin temp of -30C ( perhaps evaporating then @-35C ~).

    Taking a look at 134a properties, at O psig (gauge) or 14.7psia it has a SST of -15deg F ( converts to approx -26degC).

    here is an extract ... for 134a

    Saturation
    Temperature Pressure
    (°F) (psia)
    -50 5.51
    -45 6.41
    -40 7.43
    -35 8.58
    -30 9.86
    -25 11.30
    -20 12.89
    -15 14.67 *** corresponds -26C SST in evap, 0 psig
    -10 16.62
    -5 18.78
    0 21.16
    5 23.76
    10 26.61
    15 29.71
    20 33.09




    This would tend to suggest ( and we know to be true) that a likely 'cabin temp' for you ( in transport we call "box temp" = RA temp and should be equal to SP setpoint temp) would be in the -18C~-20C neighbourhood at 0psig gauge.
    Same was true in approx values for its predecessor R12 despite the many myths of trucks going to -30C box in " the ould days" ....

    404a is a common refrigerant for low temp nowadays. In transport , rated down to -29C @38C ambient. Magnum Reefer using Copeland Digital scroll rated to -35C on ISO boxes. There are other refrigerants too.

    You sort of answer your own concerns about risk of atmospheric air ingress at vaccum conditions on system low side. Gaskets, o rings and the crank shaft seal are vulnerable.
    Many people forget shaft seal is " double acting" - it keeps HP gas in, at low side system positive pressures ( above atmospheric) but is also intended to keep air out once sump area runs below 0 psi gauge.
    Your system must be by and large hermetic so your risks are less than open drive, splits, etc.

    Hope this helps a bit ....

    regards
    T-P
    Remember what Augustus once said:
    "festina lente" - make haste, slowly!

  3. #3
    Join Date
    Jul 2006
    Location
    Dubai
    Posts
    6
    Rep Power
    0

    Re: R134 refrigeration systems

    Thanks, thermo prince. That was quite useful. We are considering R404 compressors.

Similar Threads

  1. My local Apprentice Training Classes
    By shogun7 in forum Training
    Replies: 12
    Last Post: 17-03-2007, 03:10 PM
  2. Refrigeration alarm systems
    By tonydeith in forum Supermarket Refrigeration
    Replies: 19
    Last Post: 27-04-2006, 01:43 AM
  3. Supermarket Refrigeration System's Settings
    By monsker in forum Supermarket Refrigeration
    Replies: 8
    Last Post: 10-04-2006, 02:18 AM
  4. What is the advantages of centeral refrigeration systems?
    By dinazor2000 in forum Supermarket Refrigeration
    Replies: 4
    Last Post: 06-02-2006, 06:54 AM
  5. Leaks in refrigeration systems
    By Carlo Hansen in forum Fundamentals
    Replies: 3
    Last Post: 01-11-2005, 12:02 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •