Thread: Solenoid valve

  1. #1
    vjaiswal's Avatar
    vjaiswal Guest

    Question Solenoid valve



    I have just started my career in Ref & AC field. I got stuck up at solenoid valve. What is its function in a chilling package?



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Solenoid valve

    A solenoid valve is a mechanical shut off valve that is either open or shut depending on if it got power to the coil or not.
    The coil is an electro magnet that creates an magnetic field when energised, this in turn changes position of the valve itself and a spring and/or pressure will return the valve to the original position when the coil is de-energised.

    As to what it's function is in your specific case is hard to tell as it all depends on which line it shuts off.
    (Liquid line-stops the refrigerant flow to the evaporators, between discharge and suction-could be for pressure equalisation pre start-up, between liquid an suction-could be to cool the compressor down, and so on, the applications are numerous)
    Last edited by The Viking; 08-12-2007 at 02:42 PM.

  3. #3
    sohail's Avatar
    sohail Guest

    Thumbs up Re: Solenoid valve

    A solenoid valve is used to control the liquid line in large air conditioning systems, it is connected between the liquid line and suction line to allow refrigerant to pass through it when the compressor is short of capacity. also it is employed in refrigerators for hot gas defrost connected from discharge line to the evaporator coil.

  4. #4
    Join Date
    Dec 2007
    Location
    Tampa, Florida U.S.A
    Age
    51
    Posts
    590
    Rep Power
    17

    Re: Solenoid valve

    If you like solenoid valves, then you will love transport refrigeration units, there all over the place. i posted a thread over in transport follow the link,

    http://www.refrigeration-engineer.co...ad.php?t=10610

    some would say its a mess,,, i say its another day for a walk in the park....
    Last edited by absolute-zero; 11-12-2007 at 03:36 AM.

Similar Threads

  1. optimum defrost gas solenoid valve setting question
    By racknovice in forum Supermarket Refrigeration
    Replies: 3
    Last Post: 14-12-2007, 06:49 AM
  2. Working of Solenoid Valve
    By Mukesh in forum Commercial
    Replies: 25
    Last Post: 22-09-2006, 01:18 PM
  3. Blistering Hot Gas Solenoid Diaphragm Issue
    By dewars_aus in forum Trouble Shooting
    Replies: 7
    Last Post: 18-07-2006, 09:37 PM
  4. Whats the prefered solenoid valve location
    By kengineering in forum Commercial
    Replies: 13
    Last Post: 04-02-2006, 12:58 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •