    Variable speed drives for single phase motors
    Gentlemen
    Here is another one which i have been wondering about for quite sometime. I have to upgrade a wing of an office building and install variable air volume diffusers to achieve my goal. This dictates that i should vary the air volume from the air handing unit as well. My problem is i should use the existing AHU and it has 3 single phase supply air fans. I have never seen a single phase inveter. Can someone tell me a brillliant idea to use.
    Re: Variable speed drives for single phase motors
    Do you have a three phase supply available in the building that you could use ?
    Split Croatia
    6,151
    You could connect these three fans in star as one three phase fan motor and regulate speed with one three phase inverter.
    49
    184
    Brian uk
    yes the existing unit is supplied with 3 phase power which they distributed each phase among the 3 fans.
    49
    184
    You could connect these three fans in star as one three phase fan motor and regulate speed with one three phase inverter if you have three phase supply.
    I understand and agree with you in principle, but i have my fears. does this really work practically. i have never seen or tried it. have you done this before or seen such an installation.
    49
    184
    I understand and agree with you in principle but i have my fears. Have you done this before or seen such an installation. does it really work practically. please let me know.
    Split Croatia
    6,151
    I didn't done that before but I don't see to many reasons why this should not be working satisfactory in practice if you carefully set min. and max. sped. It is similar to conventional PWM by thyristor or triac in conventional fan speed regulators
    This could be of some value to you:
    http://tinyurl.com/3yb7sr
    http://tinyurl.com/yswttm
    http://tinyurl.com/387tge
    http://tinyurl.com/2lybnj
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Mar 2007
    394
    alternatively you could use a motorised damper in conjunction with a static pressure sensor to meter the air. Although this would involve some clever control.
    You could also use a single phase stepped speed control (transformer type) or a three phase version but you would have to introduce protection on the transformer output side on each.
    Phase chopper speed controllers are available for single phase applications but they are generaly only suitable for low load/ torque.
    all that aside I would rip out the three fans and put a 3 phase fan in
    good luck
    TRASH101's Avatar
    Mar 2007
    394
    Nikes idea will work but....
    an invertor will probabley pickle itself as you have a greater scope for phase balance faults as the 3 fans will inevitabley load up differently (especially when speed changes occur). My advice is dont do it unless you have time and money to spare
    Split Croatia
    6,151
    Quote Originally Posted by TRASH101 View Post
    This is exactly what the fan motors is, low torque and load is rising proportionally with speed.
    If it is compressor, than I should be worried!
    But as you said "advice is dont do it unless you have time and money to spare"
    49
    184
    Thank you guys for all the insights that you are giving me. This forum is such a good idea.
  1. Replies: 15
    Last Post: 17-04-2009, 03:50 PM
  2. Thermo King OptiSet
    By REEFER-TEK in forum Transport
    Last Post: 06-12-2007, 07:23 PM
  3. Variable speed screw compressors
    By Friobernal in forum Industrial Compressors
    Last Post: 14-11-2004, 09:28 AM
  4. Variable speed fridge compressors
    By Brian_UK in forum Air Conditioning
    Last Post: 18-05-2002, 11:37 PM