    How did I know the TEV's were wrong?


    Also, Tom Richardson... your cold control settings are very incorrect.


    With properly applied expansion devices for your application, you want the cold control to cut out the compressor (or solenoid valve, whichever applies) when the coil temperature reaches about 22degF, if I recall our previous discussions regarding the system balance (condensing unit capacity divided by unit cooler capacity @ 1degF T.D.)

    Set the cold control to cut out @ 22-24F, and cut in @ 38F (the cut-in being your highest desirable temperature that youwant to maintain). Your differential on the cold control is going to be about 16 degrees F.

    It seems perhaps y'alls reasoning of setting the cut-out @ 32F was to prevent a frosted over coil. The coil is a air defrost coil. Yes, frost is going to form. The off cycle is what defrosts it.

    Last edited by herefishy; 23-06-2003 at 03:18 PM.

Similar Threads

  1. Leaking frost free fridge-freezer
    By diment01 in forum Domestic
    Replies: 5
    Last Post: 22-06-2006, 11:49 PM
  2. Frost Project
    By JimmyMurphy in forum Domestic
    Replies: 1
    Last Post: 10-06-2006, 06:00 AM
  3. frost on compressor pipes
    By gabyz in forum Domestic
    Replies: 4
    Last Post: 17-05-2006, 05:09 AM
  4. distributor frost
    By Lc_shi in forum Fundamentals
    Replies: 1
    Last Post: 04-03-2006, 08:12 AM
  5. frost free's the death knell!!
    By billyfridge in forum Domestic
    Replies: 5
    Last Post: 20-06-2005, 10:58 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •