Results 1 to 50 of 237
Thread: 404a high pressure?
Threaded View
-
05-12-2007, 08:58 PM #11
Re: 404a high pressure?
the box is up to 45f and i just checked the other readings,,,
evap in 49f
evap out 44f
cond in 61f
cond out 87f
suc temp after evap 46f
scu temp before comp 54f
rec temp 98f
rec pressure 280
suc pressure 50
shouldnt the low side pressure have gone up? and yes,, im sure i turned it one full turn ccw
Similar Threads
-
Compressor loading, cooling, and range of operation.
By Air duster in forum FundamentalsReplies: 10Last Post: 02-04-2008, 08:39 AM -
fun quiz
By Brian23 in forum New to REReplies: 6Last Post: 02-10-2007, 10:18 PM -
High Side Pressure is ...
By SULTAN in forum Trouble ShootingReplies: 5Last Post: 14-08-2007, 12:53 PM -
High pressure reading before and after condenser coil
By Cofreth in forum RefrigerantsReplies: 6Last Post: 18-11-2005, 04:30 PM