Thread: Lennox KNHK 43E
-
27-11-2007, 10:04 PM #1
Lennox KNHK 43E
Hi All
Attended site to complaints of Lennox air cooled unit tripping out.
Checked over found motor protection device stopping compressor.
Bypassed MPD for a short period of time to find the low/high side refrigerant pressures doing hardly nothing.
Also found paint on compressor head to be badly cracked.
Could anyone help me with this problem.
-
27-11-2007, 10:17 PM #2
Re: Lennox KNHK 43E
Sounds like the compressor is not starting up properly.
Check the capacitors and starting relay.
Then repaint the comp.
ChillinIF AT FIRST YOU DON`T SUCCEED.
DESTROY ALL EVIDENCE THAT YOU TRIED!
and go get a cuppa
-
28-11-2007, 09:25 AM #3
Re: Lennox KNHK 43E
Chillin Out
The compressor is 3 phase.
No cappys and relays on this one.
CoolKids
-
28-11-2007, 11:15 AM #4
Re: Lennox KNHK 43E
CoolKids
I presume this is a semi and from the info it sounds like the compressor has been getting pretty hot.
If there is little difference between suction and discharge I would say the valves are shot and therefore not pumping and very little cold gas coming back to cool the windings causing the thermistor relay to trip.
Pull the compressor out and replace with a new or rebuilt one.
Paul
-
28-11-2007, 07:34 PM #5
Re: Lennox KNHK 43E
CoolKids
PaulZ is absolutely correct.
On any recip if there is little or no difference between the suction and discharge pressures.
Then it's a safe bet that the compressor is not compressing the refrigerant vapour. And the first thing to suspect is the valves being worn and no longer being gas tight. Also as a consequence of passing discharge valves. High head temperatures can be experianced (badly cracked paint on the head!)
Also as Paul mentioned, semi hermetic compressors rely on the cooling effect of the suction gases. Flowing through the windings to
cool the motor.
Dependant on wether you or your collegues strip and rebuild these comps?
Will determine your next move.
Grizzly
-
28-11-2007, 09:29 PM #6
Re: Lennox KNHK 43E
Grizzly& PaulZ
Thanks for your help.
Cheers
CoolKids
Similar Threads
-
lennox heat pump kfhk 28 vfc
By cool it in forum Air ConditioningReplies: 11Last Post: 23-02-2007, 07:34 PM -
Lennox Heat Pumps !
By cool it in forum Air ConditioningReplies: 4Last Post: 21-12-2006, 09:39 PM -
Lennox fan coil unit question
By THERMOACC in forum FundamentalsReplies: 2Last Post: 17-02-2006, 10:31 PM -
Lennox outdoor unit
By frankmcbride in forum Air ConditioningReplies: 7Last Post: 16-03-2004, 07:57 PM