    After fixing a leak on commercial unit, using R22 COMPRESSOR would not start. What do u think went wrong ?



  2. #2
    Join Date
    Jun 2007
    Location
    Cyprus
    Age
    73
    Posts
    252
    Rep Power
    17

    Re: Failed Compressor

    Hi,

    We need a bit more information regarding the circumstances. Where was the leak you fixed, was it a brazed repair, how did you deal with the system after fixing the leak (evacuate and re-charge)? Was the compressor already overheated when you got to the site - perhaps due to running low on gas ... That kind of thing.

    Regards,
    Trevor

  3. #3
    Join Date
    May 2007
    Location
    Northants
    Posts
    290
    Rep Power
    18

    Re: Failed Compressor

    Hi

    When you say the compressor would not start was it because it was tripping the power supply, have you checked there is a power supply to the compressor, has it tripped a safety circuit, did you leave a valve shut??

    CB

  4. #4
    Join Date
    Dec 2006
    Location
    Mansfield
    Age
    57
    Posts
    231
    Rep Power
    0

    Re: Failed Compressor

    Hi
    Are all the windings present & correct, the first thing maneuropes do when low on gas is overheat and go out on internal protection.
    Let the comp cool completely then carry out the proper checks etc.
    I've been to lots of sites where engineers have diagnosed maneuoropes gone, switched on comp & hey presto it runs but short of gas.

    Hope this helps


    PP

Similar Threads

  1. Testing Inverters
    By fridge doctor in forum Air Conditioning
    Replies: 38
    Last Post: 15-06-2011, 06:52 AM
  2. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  3. Mitsubishi compressor lock
    By marc5180 in forum Air Conditioning
    Replies: 29
    Last Post: 08-10-2007, 05:48 PM
  4. Compressor pumping efficiency
    By shogun7 in forum Fundamentals
    Replies: 0
    Last Post: 25-02-2004, 10:50 PM
  5. Compressor failure...... cause
    By herefishy in forum Technical Speculations
    Replies: 8
    Last Post: 06-12-2002, 12:15 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •